[RE-wrenches] Aux Output on Outback Devices

William Miller william at millersolar.com
Fri Dec 5 22:10:04 EST 2014


Jay:

 

Is this true for an FX manufactured in 2003?  What version manual is this from?

 

Wm

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Friday, December 05, 2014 5:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Aux Output on Outback Devices

 

Hi William

 

Page 23 of the VFX manual states " will reset if short circuited, no fusing is required". 

 

Jay

Peltz power



 


On Dec 5, 2014, at 5:01 PM, "William Miller" <william at millersolar.com> wrote:

Jay:

 

I suspect shorting the Aux leads will kill an FX inverter.  We traced the Aux PCB traces to the scorch marks on the control board, so it seemed pretty clear we had tested the scenario.

 

William

 

 

<image003.jpg>
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Friday, December 05, 2014 4:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Aux Output on Outback Devices

 

Hi William

 

Supposed to be. 

I've tried them with too large of a relay and wouldn't work ( the relay that is). Dead short would be the same. 

 

But i did have a VFX 3648 many years ago that had 48v on the aux output. Stumped the hell out of outback. While talking to tech, they had me short the aux wires, and poof 1 dead inverter. 

 

Jay

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141206/ea3c5d6e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141206/ea3c5d6e/attachment.jpg>


More information about the RE-Wrenches mailing list