[RE-wrenches] Aux Output on Outback Devices

William Miller william at millersolar.com
Fri Dec 5 19:57:20 EST 2014


Jay:

 

I suspect shorting the Aux leads will kill an FX inverter.  We traced the Aux PCB traces to the scorch marks on the control board, so it seemed pretty clear we had tested the scenario.

 

William

 

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Friday, December 05, 2014 4:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Aux Output on Outback Devices

 

Hi William

 

Supposed to be. 

I've tried them with too large of a relay and wouldn't work ( the relay that is). Dead short would be the same. 

 

But i did have a VFX 3648 many years ago that had 48v on the aux output. Stumped the hell out of outback. While talking to tech, they had me short the aux wires, and poof 1 dead inverter. 

 