At this time so much has changed i would do nothing. I have not had any
issues with OB like this since the introduction. I have had boil outs but
always due to incorrect settings or defective auto water refillers. How
offen was the water checked.
On Nov 18, 2014 7:16 AM, "Drake" <drake.chamberlin at redwoodalliance.org>
wrote:
> Hello Wrenches,
>
> An MX 60 boiled a 24 volt bank of 4 Trojan L-16 batteries last summer. The
> batteries all checked out to be in good shape. It is not totally clear that
> the CC was not set to auto equalize, but the EQ voltage was only set at
> 31.0 V.
>
> The battery bank has been replaced by 8 Full River L-16 AGM batteries. The
> parameters have all been reset for AGM with EQ disabled. The homeowners are
> concerned that the charge control may not work, and damage their new
> battery bank.
>
> If there is a problem with the CC, it is very intermittent. Has anyone
> ever seen an intermittent MX 60?
>
> Outback tech support says if we send it in they will update the firmware
> for $90, and do a 24 hour bench test. It appears that the firmware update
> will not do anything useful for this off grid system. There are no new
> boards available for this unit. I'm not sure if the bench test will show up
> an intermittent problem.
>
> Has anyone had this situation before? Would it be better to:
>
> - Replace the CC
> - Send the CC to Outback
> - Do nothing
>
> Thank you,
>
> Drake
>
> Drake Chamberlin
>
>
>
>
>
> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
> Solar PV 740-448-7328 <740-448-7328> *http://athens-electric.com/
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141118/1466e42c/attachment.htm>
More information about the RE-Wrenches
mailing list