I think I'm a bit confused on this point. I can't seem to find the code
that specifically exempts the GEC requirement for inverters of ungrounded
PV systems. The only exception I can find is only for AC PV modules (2014
NEC 690.47 (C) ).

I just looked in the installation manual for Solectria's new TL inverters
and found this:
"Per NEC 690.47, a GEC must be installed, and the Grounding Electrode
Terminal (GET) conductor must be sized in accordance with NEC article
250.166."

What am I missing?

Thanks,

Dana

Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com
dana at ecotechenergy.com
360.318.7646

On Tue, Oct 28, 2014 at 11:30 AM, Rebekah Hren <rebekah.hren at o2energies.com>
wrote:

> If you are on 2014:
>  690.47(B)
>
> An ac equipment grounding system shall be permitted
>
> to be used for equipment grounding of inverters and other
>
> equipment *and for the ground-fault detection reference for *
>  *ungrounded PV systems.*
>
> and 690.47(C)(3)
>
> *For ungrounded systems, this con**ductor shall be sized in accordance
> with 250.122 *and shall
>
> not be required to be larger than the largest ungrounded
>
> phase conductor.
>
> On Tue, Oct 28, 2014 at 2:22 PM, Gary Willett <
> Gary at icarussolarservices.com> wrote:
>
>> Kirk:
>>
>> A DC grounding electrode conductor (GEC) is not required for inverters
>> that do NOT have a ground reference for the PV+ and PV- conductor(s) from
>> the PV array.
>>
>> A GEC is not required if the string inverter is one of the new TL
>> (transformerless) types.  Also, this applies to micro-inverters such as the
>> new Enphase M250 and later versions of the M215.
>>
>> Where this applies, only a properly sized equipment grounding conductor
>> (EGC) is required.
>>
>> The EGC is sized according to [NEC 690.45] and can be a minimum of #14AWG
>> when not exposed to damage, or #6AWG when exposed to potential damage.
>>
>> Regards,
>>
>> Gary Willett PE
>> Icarus Engineering LLC
>>
>>
>> On 10/28/14, 12:53 PM, Kirk wrote:
>>
>>> Hi,
>>> I'm on a jobsite without my code book. Could someone tell me where in
>>> the code ungrounded systems do not require the inverter GEC? Basically my
>>> onsite electrician doesn't believe me. Thanks.
>>>
>>> Kirk Herander
>>> VSE
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>>> org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
> Tel: 336.266.8800
> http://o2energies.com/
> Project Engineer
> NABCEP Certified PV Installation Professionalâ„¢ 091209-85
> NC Licensed Electrical Contractor
>
> This message, together with any attachments, is intended only for the
> named recipient(s).   It may contain confidential or privileged information
> that may be exempt from disclosure under applicable law.  If you are not
> the intended recipient(s), you are notified that the disclosure,
> dissemination, distribution, copying, storing, or other use of the contents
> of this message or its attachments is strictly prohibited.  If you receive
> this message in error, or are not the named recipient(s), please notify the
> sender at either the email address or telephone number above and delete
> this email from your computer.  Thank you.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141103/4aaa790a/attachment.htm>


More information about the RE-Wrenches mailing list