[RE-wrenches] magnum question
Baxter, Gary
gbaxter at sensata.com
Fri Oct 31 18:44:03 EDT 2014
Follow up with Jay,
We thought it might help others to post what we found with Jay's system. This was a Magnum MS4024PAE model that is 120/240 split phase input and output. We describe this unit as 2-2k units in series inside one unit with a two winding transformer basically an autoformer.
The issue Jay was having was a "Overtemp" fault when charging from generator after an hour or so. The first tech suggested turning down the charge rate to 70% which solved the issue but didn't answer the question of why the unit was in "Overtemp". The first suspicion was there was 120v into the inverter which will cause the transformer to run on half the windings and overheat at full charger output. It is perfectly acceptable to input 120v to the MS-PAE (either leg) and it will charge and the output will be 240v but the charge rate should be reduced. The voltage measurement to the input terminals was 240v so that issue was not suspected anymore.
What Jay found was one pole of the 240v breaker from the generator was bad. What made it hard to troubleshoot and the reason for the post is that the MS-PAE will accept 120 or 240 input but always convert to 240 output. When measuring the input to a MS-PAE you should remove the wires from the terminal block and take the readings on the wires. The sense transformer on the inverter input will make the input look like 240v but no current on one leg will overheat the transformer. With the wires removed the voltage measurement will show there is no 240v available.
Gary
Gary Baxter
Product Manager
Magnum | Dimensions
2211 West Casino Rd.
Everett, WA. 98204
Office 425.353.8833 | Mobile 425.501.0289 | Fax. 425.353.8390
Please Note My New Email Address:
gbaxter at sensata.com | www.magnumenergy.com
A Sensata Technologies Business Unit
-----Original Message-----
From: Baxter, Gary
Sent: Thursday, October 23, 2014 9:50 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] magnum question
Hi Jay,
Sorry you didn't get help. Let me know what you need and I will get you an answer.
Gary Baxter
Product Manager
Magnum/Dimensions
> On Oct 23, 2014, at 9:19 PM, jay peltz <jay at asis.com> wrote:
>
> HI All,
>
> Does anyone have a person at Magnum in engineering or higher up than tech support.
>
> I've got a problem with an inverter that tech support won't or can't help with.
>
> thanks
>
> jay
>
> peltz power
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list