[RE-wrenches] Passive Battery Venting

Drake drake.chamberlin at redwoodalliance.org
Wed Oct 29 20:19:20 EDT 2014


Hi Daniel,

I typically vent them the way you do, which will allow any small 
amount of hydrogen out. The customer is absolutely adamant about 
venting these to the outside. I will cooperate so long as his method 
doesn't compromise the system through cooling the batteries 
unnecessarily in the dead of winter.

He is a lawyer and came to the conclusion of the need for venting to 
the outside from reading the NEC which says that sealed batteries 
"require the same amount of ventilation" as liquid lead acid 
batteries. The code also says to vent appropriate to battery 
technology, so the code says two conflicting things. On the other 
hand, it doesn't say that liquid electrolyte batteries need to be 
vented to the outside. They will sure stink if you vent them to the inside.

Drake

At 09:54 AM 10/29/2014, you wrote:
>I just re-read the original post Drake. These are AGM batteries. Do you have
>a "belt, suspenders,...then a rocket pack" type of client here?
>
>We typically vent our AGM boxes with small louver vents top and bottom to
>allow the batteries to ventilate for cooling purposes, not H2 concerns.
>
>With Regards,
>
>Daniel Young,
>NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13
>
>-----Original Message-----
>From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
>Behalf Of Ray Walters
>Sent: Tuesday, October 28, 2014 11:12 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] Passive Battery Venting
>
>That's why we usually have the batteries in a garage, basement, or out
>building that is not open to the living space.
>I've seen some cases of very well sealed and insulated enclosures allowing
>batteries to over heat, and also build up a lot of acid damaged connections.
>Boxes I've seen with more air space and less sealing don't get this build
>up, but you're correct: they do occasionally allow H2S into the surrounding
>area.
>
>R.Ray Walters
>CTO, Solarray, Inc
>Nabcep Certified PV Installer,
>Licensed Master Electrician
>Solar Design Engineer
>303 505-8760
>
>On 10/28/2014 8:10 PM, Jerry Shafer wrote:
> >
> > We do what we can to seal the enclosure so if or when a battery fails
> > and really gasses off the two vents on the same wall regardless of
> > wind direction will vent the gas. If it is not sealed then the gas can
> > travel through out the area this is not advised.
> >
> >
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
>
>
>
>-----
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 2012.0.2247 / Virus Database: 4031/7973 - Release Date: 10/29/14
>
>-----
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 2012.0.2247 / Virus Database: 4031/7973 - Release Date: 10/29/14
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org



More information about the RE-Wrenches mailing list