I do agree steel and copper/brass is to expensive for the possible return.
On Oct 28, 2014 4:10 PM, "Jerry Shafer" <jerrysgarage01 at gmail.com> wrote:
> We do what we can to seal the enclosure so if or when a battery fails and
> really gasses off the two vents on the same wall regardless of wind
> direction will vent the gas. If it is not sealed then the gas can travel
> through out the area this is not advised.
> On Oct 28, 2014 4:06 PM, "Ray Walters" <ray at solarray.com> wrote:
>
>> That's an interesting idea, but all the failed designs they illustrate
>> don't show the way we usually do it. We don't even bother with an inlet,
>> as most battery boxes have enough gap around the door to provide intake
>> air, then the exhaust comes off the top with several feet of rise to
>> prevent back drafting. If its in any space that H2s may be a problem
>> (living space), we always add a Zephyr Power vent which has a back draft
>> preventer. Even if the Zephyr fails, there will still be passive air flow
>> up the pipe past the fan.
>> I see 4 problems with their setup:
>> 1) Large Copper pipe is really expensive, and steel is hard to work with
>> and fittings are expensive.
>> 2) Metal pipe is not only thermally conductive, its also electrically
>> conductive. I try to avoid unnecessary conductors in the battery box.
>> 3) Metal pipe will corrode when exposed to H2S and battery acid. That's
>> why we always use plastic.
>> 4) Their suggested pipe size (1" outside pipe) are way too small to
>> provide venting for any more than a couple of golf cart batteries.
>>
>> Basically, heat exchanger = good idea, but their version = not.
>>
>> As for the battery pass through connectors: they seem to be adding
>> unnecessary connections, and would also prevent using conduit. I'd guess
>> they're not UL listed, so that whole idea is also code compliant. Duct
>> seal will prevent the H2S from going up the conduit into the DC load center.
>>
>> They're trying to seal the box too much; the only time you could actually
>> have an explosive build up of H2S is if you sealed every gap on the battery
>> box. I think its easier and safer to keep the gaps, and if your venting
>> fails, at least it won't blow up or over heat.
>>
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer,
>> Licensed Master Electrician
>> Solar Design Engineer303 505-8760
>>
>> On 10/28/2014 4:28 PM, Drake wrote:
>>
>> Hello Wrenches,
>>
>> A client wants to use a passive battery venting method with a heat
>> exchanger to the outside for his bank of Full River AGM batteries. Below is
>> a link to one site that recommends this method. Has anyone used this
>> method?
>>
>> http://www.bdbatteries.com/hydrogenventing.php
>>
>> My main concern for about the batteries is that they not get cold and
>> lose capacity during the short days when storage is most needed.
>>
>> He would also like to connect the terminals inside the box to a pass
>> through jumper http://www.bdbatteries.com/lugs.php?id=269 and then run
>> the cables, without conduit, to the inverter. As far as I know, conduit is
>> always required on the battery cables even if fuses are used in the battery
>> box. Has anything changed?
>>
>> Thanks,
>>
>> Drake
>>
>> Drake Chamberlin
>>
>>
>>
>>
>>
>> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
>> Solar PV 740-448-7328 <740-448-7328> *http://athens-electric.com/
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:www.members.re-wrenches.org
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141028/dd6222f2/attachment.htm>
More information about the RE-Wrenches
mailing list