[RE-wrenches] Interconnection with Generator

Aaron Mandelkorn reosolar at gmail.com
Tue Oct 28 11:20:28 EDT 2014


I always connect to the utility side of the transfer switch. Since the transfer switch is a listed electrical enclosure it is the best option I have used. 

Aaron

Aaron Mandelkorn
Owner/Solar Specialist
Renewable Energy Outfitters
719-221-5249
970-596-3744
www.reosolar.com
reosolar at gmail.com


> On Oct 28, 2014, at 8:48 AM, Corey Shalanski <cshalanski at joule-energy.com> wrote:
> 
> Wrenches,
> 
> We frequently encounter residences with backup generators. The question that arises: how should the PV system be interconnected?
> 
> I have searched the archives and found some good information about this subject, but nothing definitive. I have fallen into the habit of broadly proclaiming that the PV system *must* be interconnected on the "utility" side of the transfer switch - in order to prevent backfeeding into the generator and thereby eliminate unintentional equipment damage. Is this concern justified? If so, should this be an absolute rule or would it depend on the generator make/model?
> 
> Thanks for any insights.
> 
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 


More information about the RE-Wrenches mailing list