[RE-wrenches] AC combiners
Dave Click
daveclick at fsec.ucf.edu
Fri Oct 24 13:39:43 EDT 2014
Bill, typically inverters have a max OCPD that can be installed on their
output, and these sizes are generally not large enough to accommodate
two same-model inverters. And manuals often note that you need to have a
dedicated OCPD anyway. At least if I were ever to double-up two
inverters on a single breaker, I'd want to make sure I had clearance
from the manufacturer to do so. Or... just buy the $75 box to combine
the two.
DKC
On 2014/10/24 11:05, frenergy wrote:
> Wrenches,
> ...its the little things. Recently someone here brought up
> the issue of combining AC outputs prior to backfeeding the "solar" CB
> in the mains panel. In the past I've run AC outs from inverters into
> a small AC dist panel, backfeeding CBs and then ran my combined AC out
> from a larger CB or the busses themselves to the backfed CB in the
> mains panel. Is this overkill?
> It does seem as though, at least for just 2 inverters, this
> could be done with just split bolts in a gutter or dedicated
> J-box....or a power distribution block?? Or...?? (no wire nuts, thank
> you) Your ideas appreciated.
> Bill
> Feather River Solar Electric
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141024/94fa9f61/attachment.htm>
More information about the RE-Wrenches
mailing list