Bill,

 

See 2011 NEC 690.14(D) or 2014 NEC 690.15(A) Utility-Interactive Inverters Mounted in Not Readily Accessible Locations.  Basically there is no maximum height restriction for inverters but there are a number of requirements for AC and DC disconnecting means.  See NEC 404.8 for maximum disconnect height of 6’ 7”…although exception No. 2 may allow the disconnect to be accessible by portable means.  I don’t know of any minimum height requirements in the code, although most (all?) string and microinverter manufacturers specify a required clearance below the inverter.  I suppose that would be the minimum. 

 

Garrison   

 

Garrison Riegel

Project Manager |  <http://www.solarserviceinc.com/> Solar Service Inc

[p] 847-677-0950 |  <mailto:garrison at solarserviceinc.com> garrison at solarserviceinc.com

 

NABCEP Certified PV Installation Professional™

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of frenergy
Sent: Tuesday, October 21, 2014 11:02 PM
To: RE-wrenches
Subject: [RE-wrenches] Mounting height

 

Wrenches,

 

        I can't seem to find a reference to the heights allowable for inverter installs, either minimum or maximum (need both).  For that matter, AC combiners, DC discos, any switchgear related to the inverter(s).

 