There is some pressure on NM specifically to postpone adoption of 690.12
until more products are available, so that may help you out. To my
knowledge, micro-inverters don't need to comply with 705.12(D)(6) since
there are no suitable products available [90.4]. Equipment does need to
be listed, and it does need to provide rapid shutdown functionality, but
it does not need to be "listed for rapid shutdown" to be code-compliant
since that isn't a thing.
String inverters generally speaking would have to have some method of
"control" within 10' of a rooftop array, like contactor combiners. I'm
interested in seeing what SMA's solution is, since contactor combiners
(as discussed earlier in this thread) aren't well suited for these
multi-MPPT inverters. I guess you can always add a second contactor but
I don't know what listed equipment is available right now (so... 90.4?).
DKC
On 2014/10/9 12:41, Randy wrote:
>
> Hi Wrenches,
>
> We are being forced to adopt 690.12 Rapid Shutdown requirement based
> on several explanations given to our industry:
>
> 1.otherwise we would be ignoring the life safety and put our fire
> fighters lives in peril
>
> 2.This product can be constructed from readily available,
> over-the-counter code compliant components. This (is) to be the
> intent of CMP4when compiling the NFPA70.
>
> We do not want to act like an industry that appears to be fighting
> against safety. And we know there are a few products that are code
> compliant, micro-inverters (don’t comply with 705.12 (D) (6) because
> there are no products), Solaredge, and Tigo (is it approved?) yet this
> is not how we choose products.
>
> And the SMA SPS inverter is not going to work in a 690.12 environment
> without complications as far as I can see.
>
> Appreciate comments that might support the right decision.
>
> Thanks,
>
> Randy
>
> Randy Sadewic
>
> Cell: 505 570-0137
>
> Randy at PositiveEnergySolar.com <mailto:Randy at PositiveEnergySolar.com>
>
> http://positiveenergysolar.com/admin/content/uploads/PES-logo-3.jpg
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *Steve Jefferson
> *Sent:* Tuesday, October 07, 2014 8:33 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] TL Inverters
>
> The first gen of TL’s did have a somewhat tight window for the DC window.
>
> However, the new SBxxxxTL-US-22 (3kW – 7700kW, with secure power
> supply) Start Voltage is 125, MPPT is 175-480 (max of 600Vdc)
>
> Also, for larger needs, the STP (12kW – 24kW) start voltage is 150,
> MPPT is 300-800V (max of 1000Vdc).
>
> SMA America, LLC
>
> Steve Jefferson
>
> Service Line Supervisor
>
> 3925 Atherton Ave
>
> Rocklin, CA 95765 - 3714
>
> U.S.A.
>
> Tel: +1 916 625 3185 (direct)
>
> Fax: +1 916 625 0871
>
> Mobile: +1 916 622 4253
>
> Email: Steve.jefferson at SMA-America.com
> <mailto:Steve.jefferson at SMA-America.com>
>
> www.SMA-America.com <http://www.sma-america.com/>
>
> cid:image001.png at 01CF1CFA.FE18BEB0
> <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be>
>
> This email and any attachments thereto may contain SMA America, LLC
> confidential, privileged and private material for the sole use of the
> intended recipient. Any review, copying, or distribution of this email
> (or any attachments thereto) by others is strictly prohibited. If you
> are not the intended recipient, please contact the sender immediately
> and permanently delete the original and any copies of this email and
> any attachments thereto. Thank you.
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *Mark Byington
> *Sent:* Tuesday, October 07, 2014 6:59 AM
> *To:* RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] TL Inverters
>
> Just a word of caution to those not having experience with SMA TL
> inverters - the larger units (7-11 kW) have an extremely narrow input
> DC voltage window. Depending on your module voltage and string
> design, all you need is a module or two to be shaded to fall out of
> the MPPT input voltage range. The smaller units (3-5 kW) with the
> Secure Power Supply don't have this problem. We no longer use these
> larger SMA TL inverters unless we can do maximum string length (e.g.
> strings of 8 for SunPower 96-cell) and there is zero shade at the site.
>
> I believe SMA is in the process of adding larger units to the line
> that has the Secure Power Supply. They added the 6 kW unit earlier
> this year, and just announced the 7 kW unit with Secure Power Supply.
>
> Mark Byington
>
> Cobalt Power Systems, Inc.
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141009/7d7b44d2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 6339 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141009/7d7b44d2/attachment.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 30736 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141009/7d7b44d2/attachment.png>
More information about the RE-Wrenches
mailing list