Just to pile on here, if you're running 4 pairs of low-voltage dc for
400' you may be better off just sticking the inverters right there at
the array and making the long run as 240Vac. #2s on each inverter output
(22A?) would work, keeping voltage drop to 1.3%. If you choose to
combine inverter outputs right there at the array (you'd need ac
disconnects there anyway) you'd have to run #3/0 for a 1.3% drop. Not
sure whether that's more feasible for you.
DKC
On 2014/10/7 16:06, Isaac Opalinsky wrote:
>
> William,
>
> What is your string configuration? The SMA TL inverters have a very
> low operating voltage window, going down to 125 Vdc, but you still
> have the issue of the disconnect.
>
> Have you looked at ABB’s (PowerOne) TL inverters:
> http://www.abb.us/product/us/9AAC179447.aspx?country=US? They can be
> programmed to operate down to 90 Vdc, and they give you the ability to
> combine upstream and have the 2 MPPT’s operate as one, allowing you to
> combine outside of the inverter and bring a single set of PV output
> conductors to the inverter’s DC disconnect:
>
> *Isaac Opalinsky *| Technical Trainer | *SunPower Corporation*
>
> Desk 443-569-3476 | Cell 443-277-6286
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *William Miller
> *Sent:* Tuesday, October 07, 2014 12:01 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
>
> Friends:
>
> If only an SMA would work here. But DC volts too low. We are using
> Solectria PVI5200TLS.
>
> We do not use PV wire. We transition to THWN-2 in conduit immediately.
>
> William
>
>
> Miller Solar
>
>
> On Oct 6, 2014, at 8:30 PM, Chris Mason <cometenergysystems at gmail.com
> <mailto:cometenergysystems at gmail.com>> wrote:
>
> I presumed SMA TL series.
>
> On Mon, Oct 6, 2014 at 10:02 PM, Jerry Shafer
> <jerrysgarage01 at gmail.com <mailto:jerrysgarage01 at gmail.com>> wrote:
>
> As i read the thread you say TL which TL SMA, AE ect. They have
> defferent dc input designs
>
> On Oct 6, 2014 12:21 PM, "jay peltz" <jay at asis.com
> <mailto:jay at asis.com>> wrote:
>
> I do believe the outback and midnite combiners have a lock hole to
> prevent exactly your concern.
>
> unauthorized access.
>
> jay
>
> peltz power
>
> On Oct 6, 2014, at 11:40 AM, William Miller wrote:
>
>
>
> Wrenches:
>
> We are getting up to speed on using transformer-less inverters. I
> have advocated long for the additional safety offered by these
> inverters but I am realizing the trade-offs with the new
> technology: The implementation gets more complicated with the
> requirement for PV wire, OCPD and disconnecting means for plus and
> minus and plus providing Arc Flash rated equipment.
>
> I am currently designing a system that will locate the PV about
> 400 feet from the residence. The system will utilize 2 Solectria
> 5200 watt inverters at the residence. I would like to provide
> disconnecting means for the 4 strings at the array, in case of any
> needed service or excavating. Preferably I’d like the
> disconnecting means to be deployable by a lay person (i.e. the
> gardener).
>
> Finding an 8 pole, arc flash, 600 VDC rated disconnect is not
> easy. I could install an Outback 8 circuit combiner with 8
> touch-safe fuse holders. The new combiners have had dead-fronts
> for a while now. The gardener needs only to have a Philips screw
> driver to open this cover. Any better ideas out there?
>
> Thanks,
>
> William
>
> <image002.jpg>
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600 <tel:805-438-5600>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> --
>
> Chris Mason
>
> NABCEP Certified Solar PV Installerâ„¢
>
> Solar Design Engineer
>
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
>
> 264.235.5670
>
> 869.662.5670
>
> Skype: netconcepts
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141007/66fd0971/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 20910 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141007/66fd0971/attachment.png>
More information about the RE-Wrenches
mailing list