Eaton has a line of disconnects that may fit the bill:
http://www.eaton.com/Eaton/ProductsServices/Electrical/ProductsandServices/ElectricalDistribution/SwitchesandDisconnects/SolarDisconnects/index.htm#tabs-2
Ryan
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of August Goers
Sent: Tuesday, October 07, 2014 11:30 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
William,
I see now from the separate post from Michael Kelly of Solectria that indeed you cannot combine your two strings with this inverter. I think that leaves you stuck with four separate disconnect switches unless someone on this list knows of a four pole DC rated disconnect switch. Or, you’ll have to switch inverters. I have never installed these Solectria inverters so I don’t know much about them.
Best,
August
Luminalt
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
Sent: Tuesday, October 07, 2014 8:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
August:
I have been told I can't combine upstream of the inverter.
William
Miller Solar
On Oct 7, 2014, at 8:03 AM, August Goers <august at luminalt.com> wrote:
William,
We have bumped into similar dilemmas when needing remote DC disconnects with TL inverters. I believe the Solectria you are using has two MPPTs? Ideally, you would keep each string separate to benefit from the dual trackers – this would mean four DC disconnects if you went with a standard product like a Square D HU361RB. If you combine each of the two strings out at the array(s) then you could get away with two disconnects, one for each inverter. Neither option is ideal.
Best,
August
Luminalt