Mark,
The only thing I would add to all your good points is the addition of a 7700 watt TL which is of course perfect to stay under the 20% for load side connection of a 200A service.
Bill
----- Original Message -----
From: Mark Byington
To: RE-wrenches at lists.re-wrenches.org
Sent: Tuesday, October 07, 2014 6:58 AM
Subject: Re: [RE-wrenches] TL Inverters
Just a word of caution to those not having experience with SMA TL inverters - the larger units (7-11 kW) have an extremely narrow input DC voltage window. Depending on your module voltage and string design, all you need is a module or two to be shaded to fall out of the MPPT input voltage range. The smaller units (3-5 kW) with the Secure Power Supply don't have this problem. We no longer use these larger SMA TL inverters unless we can do maximum string length (e.g. strings of 8 for SunPower 96-cell) and there is zero shade at the site.
I believe SMA is in the process of adding larger units to the line that has the Secure Power Supply. They added the 6 kW unit earlier this year, and just announced the 7 kW unit with Secure Power Supply.
Mark Byington
Cobalt Power Systems, Inc.
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141007/128f1110/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: FRS_working_logo, 50%.JPG
Type: image/jpeg
Size: 8424 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20141007/128f1110/attachment.jpe>
More information about the RE-Wrenches
mailing list