Flipping through the '04 plumbing code I see a few slopes called out
(1/4" per 1' for fixture vents, 1" per 1' for circuit vents, 1/2" per 1'
for combination drain/vent...). Fixture vents have a maximum distance of
a few feet from fixture trap to vent, but I don't think this prevents
you from then running that vent horizontally. 916.2 states that for
vents other than stack vents or vent stacks if your vent is >40' you
need to upsize the whole vent pipe (tough to do for an existing
building, of course). Stack vents have a "maximum developed length" of
100' for a 1.5" vent which should be enough space to get away from under
the PV. I don't see any slope requirements specifically for stack vents
but my non-plumber's eye may be missing something.
The stack vent sizing Table 916.1 appears (in part) here too and it
looks like the tables match up to a 2.5":
http://www.engineeringtoolbox.com/drainage-vents-d_1110.html
DKC
On 2014/9/24 10:19, Jason Szumlanski wrote:
> I am unable to find anything in the Florida code that precludes
> covering a plumbing vent. The code does require the vent to be 6"
> above the roof surface I believe.
>
> I was unable to determine if these vents need to be vertical with no
> bends in the attic. Obviously you wouldn't want to create a trap in
> the attic, but a couple of 45's to relocate a plumbing vent to
> accommodate more PV seems like a desirable thing to do sometimes. Does
> anyone know if these can be relocated, i.e. to an adjacent roof surface?
>
> On my own home I had a vent to deal with. I broke out my saws-all,
> split the lead like a banana and peeled it back, cut the pipe at an
> angle, and folded the lead back into the pipe after applying sealant
> between the lead and pipe. There is a 1" gap between the rim of the
> pipe and the back of the module. My theory on this working safely is
> that, a) there will be far less rainwater falling in and around this
> pipe with a module over it, and b) it is about 24" from the roof ridge
> and there is a module over it so there will be very little water
> sheeting down from above the vent. Code notwithstanding, I felt this
> was a solid method on my own home, and I have inspected it after 6
> months of Florida downpours and found no issues.
>
>
> Jason Szumlanski
>
> Fafco Solar
>
>
> On Wed, Sep 24, 2014 at 6:38 AM, Bill Loesch <solar1online at charter.net
> <mailto:solar1online at charter.net>> wrote:
>
>
> Bruce, August, et al,
>
> This is but one more example of confusing terminology. A plumbing
> vent is not an exhaust vent!
>
> A plumbing vent (what August calls a cold vent) is provided to
> allow the sanitary drain traps (and perhaps more) to operate
> properly. Without the properly functioning traps you would have
> sewer gas smell and sewer gas from the plumbing fixtures. This was
> commonplace when indoor plumbing was introduced to early adopters.
>
> An exhaust vent is another animal entirely. An exhaust vent
> carries the combustion products to a suitable exterior location
> for dilution with ambient air. With the advent of power vented
> combustion appliances, a direct vent (one that takes in combustion
> air from the outside and naturally exhausts combustion products to
> the outside) is IMHO the only responsible way to install any power
> vented appliance in a freezing climate. (Power vented appliances
> come in both condensing and non-condensing flavors-they can
> penetrate the side wall or the roof). Originally, two separate
> pipes (with two independent properly separated penetrations) was
> used. That technique is still often used today. More recently
> concentric vents have been introduced both for condensing and
> non-condensing applications. A concentric vent can simplify some
> installations by putting the exhaust pipe inside a larger air
> intake pipe allowing for one, albeit larger, penetration. As you
> might imagine if the exhaust flow is hindered/diverted/redirected
> by an inappropriately located solar module combustion gasses will
> be re-ingested into the intake air. Not good for equipment
> performance. My understanding is the power vented _appliance
> manufacturer_ dictates what kind of separation/clearances are
> needed with their product. My guess is you find they want at least
> a foot of separation between the top of the " inverted cone" and
> the module. Probably not what you had in mind for an aesthetically
> pleasing installation.
>
> I hope this helps,
>
> Bill Loesch
> Solar 1 - Saint Louis Solar
> 314 631 1094 <tel:314%20631%201094>
>
> On 23-Sep-14 6:54 PM, August Goers wrote:
>> Bruce and All, Sorry, I hit send before I had a chance to
>> complete my thoughts. What I meant to say was that I've found
>> AHJs often allow us to cover cold plumbing vents but I've never
>> tried or had any luck with covering hot vents including
>> condensing boiler PVC vents. Once again, if in doubt you could
>> see what the plan checker or inspector thinks. Best, August
>> -----Original Message----- From: August Goers
>> [mailto:august at luminalt.com] Sent: Tuesday, September 23, 2014
>> 4:15 PM To: 'RE-wrenches' Subject: RE: [RE-wrenches] Modules over
>> vents Bruce, I'll send you the CA plumbing code vent section
>> offlist (attachment too large for this list). The way I read the
>> code is that you technically can't cover any type of plumbing or
>> hot vent. However, and I've run into little resistance from AHJs
>> in the Bay Area by covering these. You might want to check in
>> with your plan checker. Best, August Luminalt -----Original
>> Message----- From: RE-wrenches
>> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
>> Bruce Leininger Sent: Tuesday, September 23, 2014 3:49 PM To:
>> RE-wrenches Subject: [RE-wrenches] Modules over vents Hi all.
>> We're designing a system on a roof that is literally infested
>> with plumbing, exhaust and combustion vents. The combustion vents
>> are PVC and none of the vents are more than 1.5' above the roof.
>> A racking company says that we can cover them with modules, since
>> the modules will be at least 4' above the roof. They have not yet
>> provided any building code references to say that this is ok. Do
>> any of you know if the building code allows this? Thanks. Bruce
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140924/dbdfaf7c/attachment.htm>
More information about the RE-Wrenches
mailing list