[RE-wrenches] Conduit supports on sloped composite shingle roofs
Chris Mason
cometenergysystems at gmail.com
Mon Sep 22 19:57:14 EDT 2014
In a hurricane region, we can't use glued supports.
Caddy supports are for flat roofs. These are 30 degree roofs.
I think I am going to use unistrut with two holes bored in it, washered
screws and sealant, and a HDG conduit clamp.
On Mon, Sep 22, 2014 at 7:49 PM, August Goers <august at luminalt.com> wrote:
> Hi Chris,
>
>
>
> There are a few common methods to run conduit along the roof surface.
>
>
>
> 1. Blocks made of Trex or another similar wood substitute with
> conduit fastened with 1-hole straps. Trex is typically only glued to the
> roof with roofing sealant (no penetrations)
>
> 2. A more professional support such as the Chem Link KnuckleHead:
> http://www.chemlink.com/index.php/chemlink-products/knuckleheads or Erico
> Caddy: http://www.erico.com/public/library/Fixing/LT1058.pdf - there are
> other manufacturers as well
>
> 3. Quickmount classic conduit comp mount:
> http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMCC-Conduit-web.pdf
>
>
>
> For residential projects we typically use Trex. For commercial projects we
> typically use the Erico Caddy. If the roof is really steep and the blocks
> won’t stay put then we use the Quickmount product.
>
>
>
> For getting through the roof we typically use a standard pipe flashing or
> a SolaDeck.
>
>
>
> Best,
>
>
>
> August
>
>
>
> Luminalt
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Chris Mason
> *Sent:* Monday, September 22, 2014 2:43 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Conduit supports on sloped composite shingle
> roofs
>
>
>
> I'm curious what methods people are using to mount, flash and stand-off
> conduit from the comp. shingle roofs. We don't do a lot of shingle, mostly
> metal and concrete, so we are less that familiar with the options. We used
> SnapNRack flashed mounts for the rail system, but they need a rafter under
> them and the conduit run will not be above rafters.
>
> As it is very hot here, I want to get some air between the conduit and the
> roof.
>
>
>
> --
>
> Chris Mason
>
> NABCEP Certified Solar PV Installer™
>
> Solar Design Engineer
>
> Generac Generators Industrial technician
>
>
>
> www.cometsolar.com <http://www.cometenergysystems.com>
>
> 264.235.5670
>
> 869.662.5670
>
> Skype: netconcepts
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts