[RE-wrenches] Sunny Island sending power to the generator??
Jarmo.Venalainen at schneider-electric.com
Jarmo.Venalainen at schneider-electric.com
Thu Sep 18 13:36:47 EDT 2014
Hi:
It is possible for a grid tie inverter connected to the output of a
battery based inverter to export energy through the battery based inverter
to the AC source. It doesn't matter is that source is the grid, a
generator, or any other AC power source.
Indeed, due to this common AC bus wiring structure inside the battery
based inverter, there is no way for the battery based inverter to prevent
this, other than disconnecting.
Here's a line diagram of a typical battery based inverter with a grid tie
inverter connected at its output.
In the diagram you can see that,
1. All the AC sources and loads are on a common AC bus consisting of only
copper wires and a couple of disconnects. . This structure of true of
all of the grid, that is, there are multitude of AC sources and loads all
on a common grid of copper wires and disconnects.
2. The only thing that the battery based inverter can do is, in charge
mode, behave like a load as it draws power from the AC bus and charges the
batteries or in invert mode adjust its AC output voltage so that it
becomes a parallel AC source with the generator and is able to supply
power to the AC bus concurrently with the generator.
Here's where it gets interesting,
3. If the battery based inverter is in invert mode and a source such as a
gird tie inverter raises the AC voltage on the AC bus, then power will
flow in reverse through the transformer and the batteries will be charged
using the grid tie inverter power as the source. This is AC coupled
charging.
4. At the same time, if the grid tie inverter raises its output voltage
above that of the generator, power will flow into the generator. The
diesel motor in the generator will in this case be under a positive load,
which is the same condition as a truck using engine brakes.
5. Unfortunately most generators are not built to operate as an engine
brake, so bad things can happen to them. For this reason, the control
algorithm in the battery based inverter will disconnect from the generator
to protect it from damage.
There is more details to this in regards how many residential loads are
on, the quality of the generator output power waveform, methods to control
the AC coupled charging, etc., but the above is the essence of how it
works.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Development Specialist - Senior
Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
"William Miller" <william at millersolar.com>
To:
"RE-wrenches" <re-wrenches at lists.re-wrenches.org>,
Date:
09/17/2014 10:20 PM
Subject:
[RE-wrenches] Sunny Island sending power to the generator??
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
Colleagues:
I was invited to troubleshoot a Sunny Island system. What I found is a
Sunny Island mini-grid system behaving oddly. The generator, when started
with the SI, would run for a few minutes and then shut down. Further
investigation revealed that the SIs were indicating that the inverters
were sending lots of power back to the generator, even with the Sunny Boy
turned off.
I don’t know if this was actually the case, nor can I grasp how this could
happen. The system was programmed as a PV/Gen only system. Fortunately I
reached an off-grid tech at SMA and we were able to resolve the issue. I
am not sure what we did but I suspect that simply rebooting the Sunny
Islands was the cure.
I post this in case any of you experience this problem and could benefit
from my experience. Also, I want to understand this better. Could it be
true that the inverters could send power to the generator? I know the
circuitry is there to sell to AC2, which is how this system would work as
a true grid-interactive system, but how did it get triggered? Was it
battery-selling to the generator? I welcome any comments.
What I am starting to think is that the Sunny Island system, like any
feature rich system, is complicated and has the potential to be less
reliable than simpler systems. On the plus side I could also think of
these systems as job security for the knowledgeable technician.
Sincerely,
William
Lic 773985
millersolar.com
805-438-5600
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140918/00c0b037/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 35391 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140918/00c0b037/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14092 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140918/00c0b037/attachment.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140918/00c0b037/attachment-0001.jpe>
More information about the RE-Wrenches
mailing list