[RE-wrenches] LiFePo4
jay peltz
jay at asis.com
Wed Sep 17 03:38:28 EDT 2014
HI Ray,
We could still use them now and for legacy systems.
I can only think it could be a big help in saving battery banks of all types.
jay
peltz power
On Sep 17, 2014, at 6:32 AM, Ray Walters wrote:
> I think if we started over fresh with our lead acid battery system designs, we would find we should have the same Battery management system requirements that you have mentioned. Those are all problems that plague lead acid as well.
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 9/15/2014 8:08 PM, Jarmo.Venalainen at schneider-electric.com wrote:
>> Hi:
>>
>> We've done some testing and operation of Lion battery banks in the 10 kWh range with our inverter chargers and so far the most important findings are:
>>
>> 1. The battery pack must have its own battery management system to:
>> a. regulate the individual cell voltages during charge and discharge
>> b. balance the cell voltages during charge and discharge
>> c. adjust cell charging voltages due to temperature variations
>> d. not provide a continuous float voltage to the battery bank
>> d. provide a built in safety cutoff disconnect, which turns off the current if for any reason either the charge or discharge current is too high.
>>
>> A series string of Lion cells, without the battery management system functions above is very likely to result in damaged cells or worse. The most likely mechanism which ultimately causes damage is individual cell temperature or cell to cell voltage imbalance.
>>
>> 2. The inverter system must be designed so that the inverter never draws so much current that the current limit circuit in the battery bank is triggered.
>>
>> 3. It may be necessary to adjust the current limit circuit as they typically respond within milli-seconds and may be triggered on simple power up as the inverter cap bank charges up.
>>
>> 4. When working with Lion, the inverter/charger should be configured so that it is a simple current limited voltage source when in charge mode. The built in battery management system should take care of the required charge cycle operation.
>>
>> 5. Whether the pack is LiFePO4, Lion polymer or other does not appear to be as important as a having a reputable brand and more importantly a well designed built in battery management system.
>>
>> The short version is that lead acid cells are amazingly forgiving with regards charging and discharging voltages, currents and temperatures. Lion cells on the other hand are amazingly sensitive and going out of bounds on any of these can and will cause irreparable damage.
>>
>> Given the sensitivity, it doesn't make sense to take on responsibility for Lion battery management.
>>
>> Management of that sensitivity and responsibility is best left to the battery bank manufacturer.
>>
>> JARMO
>> _____________________________________________________________________________________
>>
>> Jarmo Venalainen | Schneider Electric | Solar Business | CANADA | Training & Development Specialist - Senior
>> Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
>> Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com | Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
>>
>> <Mail Attachment.jpeg>
>> *** Please consider the environment before printing this e-mail
>>
>>
>>
>> From: "William Miller" <william at millersolar.com>
>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>,
>> Date: 09/15/2014 04:27 PM
>> Subject: [RE-wrenches] LiFePo4
>> Sent by: "RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
>>
>>
>>
>> Wrenches:
>>
>> Does anyone have any experience with Lithium Ferrous Phosphate cells? What are your experiences? I am looking at an installation tomorrow and would like some input.
>>
>> Thanks in advance.
>>
>> William Miller
>>
>> <Mail Attachment.jpeg>
>> Lic 773985
>> millersolar.com
>> 805-438-5600
>>
>>
>> ______________________________________________________________________
>> This email has been scanned by the Symantec Email Security.cloud service.
>> _____________________________________________________________________________________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140917/3b3f5098/attachment.htm>
More information about the RE-Wrenches
mailing list