Hi William,
Please remember the GTI is not compatible with SW models manufactured
prior to 2002.
Rgds.
_________________________________________________________________________________________
Eric Bentsen | Schneider Electric | Customer Care Center | Advanced
Technical Support | Technical Support Engineer
Phone: 866-519-1470 option #1 | Schneider Electric Support Center:
+800-640-0770
Email: eric.bentsen at schneider-electric.com | Site:
www.schneider-electric.com/solar |
Address: 1660 Scenic Ave. Costa Mesa, CA 92626
How am I doing? Please e-mail my manager with any feedback at:
Jim.Houlik at Schneider-electric.com
*** Please consider the environment before printing this e-mail
From:
"William Miller" <william at millersolar.com>
To:
"'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>,
Date:
09/09/2014 09:06 AM
Subject:
Re: [RE-wrenches] Grid-tied Trace SW
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
Russell:
I am curious, how do you perform anti-islanding tests?
The SW4024 should work great with a 3.3 kW array. Due to battery and
inverter inefficiencies you would never see the full 3.3 sell back any
way, which is less than the rating of the inverter.
The SW4024 was UL listed at one time but the listing was removed due to
failure to apply the testing regimen properly, if I remember correctly. We
were not required to retrofit existing installations by adding the GTI,
only to add them to pending installations. Our utility lost a lot of
applications during that era and years later, when forced to reapply, they
accepted the SWs without GTIs. If you really want one, I have one in the
shop I would sell cheap, but I don’t have much faith in the design.
Lastly, I can’t comment on the efficiency of the SW versus a modern GTBB
inverter. That question would justify some research. If the SW is
significantly less efficient than, say, a Sunny Island, the impetus may be
there to upgrade.
William Miller
Lic 773985
millersolar.com
805-438-5600
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Russell Mueller
Sent: Tuesday, September 09, 2014 7:43 AM
To: RE-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] Grid-tied Trace SW
Hello Esteemed Wrenches,
I have a prospective client who has an old GTBB system using a Trace SW --
it was permitted and signed off by the utility way back when and has been
operational ever since. It's a Trace SW 4024 that's feeding the grid
through a Trace T-240 transformer -- I didn't see a GTI. All he wants me
to do is replace his failing array (which would increase his array size
from 1152W to 3300W) -- not pull a permit, not change the BOS other than
to add a 2nd charge controller.
The original question that lead me to write this post is whether the
SW4024 can handle the full 4kW sell-back onto the grid -- I couldn't find
any specs on that on the web.
But the question I have now is whether the Trace SW is UL1741 compliant. I
didn't think to do an anti-islanding test before I left the site. If it's
not, then I'm thinking maybe I should insist that he change out his
inverter for a modern one, or I'll pass on the job. If it fails an
anti-islanding test (which I'll do next time I'm in his neighborhood),
then the dangers are obvious, and I don't want the liability.
What would you all do in this situation? Do any of you have experience
with grid-tied SWs -- any advice?
Thanks,
Russ
--
Russell Mueller
NM EE98 Electrical Contractor, license #382671
NM ER1J Journeyman Electrician
Photovoltaic Designer / Installer
BUFFALO SOLAR LLC
Taos, New Mexico
575-770-4877
russ at buffalosolartaos.com
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140909/593ae5b2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140909/593ae5b2/attachment.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 18959 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140909/593ae5b2/attachment-0001.jpe>
More information about the RE-Wrenches
mailing list