[RE-wrenches] Rapid shutdown questions

Will White William.White at rgsenergy.com
Wed Aug 27 10:12:38 EDT 2014


That’s correct it’s a manual disconnect and I agree it totally defeats the purpose but some AHJ’s are accepting that it’s within 5’ of entering the building and nowhere in the code does it say it has to be readily accessible.

We had one AHJ make us put the disconnect on the side of the house about 15’ feet up.  I believe that photo was in the last issue of SolarPro.  It was the dumbest thing we’ve ever had to do and it looks ridiculous but that’s what the inspector wanted.

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Wednesday, August 27, 2014 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rapid shutdown questions

Hi Will,

Yes I'm sure AHJ's will be all over the place for a while here in Colorado.  To clarify, is this a manual disconnect in the attic?  If so, that is really missing the whole idea of a rapid shutdown.

Thanks

On Wed, Aug 27, 2014 at 7:47 AM, Will White <William.White at rgsenergy.com<mailto:William.White at rgsenergy.com>> wrote:
Our experience in MA with rapid shutdown unfortunately varies with AHJ.  Some are letting us put an Eaton NEMA 4 disconnect on the roof next to the array.  Some are letting us put a disconnect in an accessible attic within 5’ of the penetration.  Some are requiring the Midnight Birdhouse remote switch which is expensive.

Rapid shutdown doesn’t apply to pole or ground mounts.

Hope this helps.

Will

Will White
Operations Manager - New England
RGS Energy


64 Main St. |Montpelier, VT 05602
tel 802.223.7804<tel:802.223.7804> | mobile 802.234.3167<tel:802.234.3167> | fax 802.223.8980<tel:802.223.8980>

RGSEnergy.com<http://www.rgsenergy.com/> | william.white at rgsenergy.com<mailto:william.white at rgsenergy.com>

Confidentiality Note: This e-mail message may contain confidential or legally privileged information and is intended only for the use of the intended recipient(s). Any unauthorized disclosure, dissemination, distribution, copying or the taking of any action in reliance on the information herein is prohibited. E-mails are not secure and cannot be guaranteed to be error free as they can be intercepted, amended, or contain viruses. Anyone who communicates with us by e-mail is deemed to have accepted these risks. RGS Energy is not responsible for errors or omissions in this message and denies any responsibility for any damage arising from the use of e-mail. Any opinion and other statement contained in this message and any attachment are solely those of the author and do not necessarily represent those of the company.





From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of Mac Lewis
Sent: Wednesday, August 27, 2014 8:32 AM
To: RE-wrenches
Subject: [RE-wrenches] Rapid shutdown questions

Hello wrenches,

I am still trying to wrap my head around how to comply with rapid shutdown in off-grid and hybrid situations.  I've got a few questions that maybe you can help with.

1.  What is a (currently listed) rapid shutdown system that will accommodate 8 strings?  I know I can do this with Midnite combiners but as I understand these aren't listed yet.
2.  On a remote pole mount, does rapid shutdown apply?  If the intent is to isolate a safe zone around an array for fire fighting, it seems as though a standard pole mounted DC disconnect can cover this concern.
3.  I estimate on a typical hybrid installation, rapid shutdown will cost at least $3000 to implement. This includes remote shunt trip battery breakers, contactors on PV side of charge controller and roof combiners, and running control cable from remote disconnect to all locations.  As of now, this would also require me to modify listed interconnection equipment.  Is this what others are finding?
4.  AC coupling with microinverters may be the easiest way to comply with most of these requirements.  However, this doesn't seem like a great alternative to the standard charge controller installation in an off-grid system.

Thanks in advance for your thoughts


--



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios: