Marco, here’s a scenario – a bit theoretical, but I’m curious to get your input since you’ve been active on this topic for a while (I’m assuming the values below are reasonably accurate – I haven’t looked at the datasheets for a while):
ABB 300’s
Enphase 215
Max Power
300
225
Max Current
1.25
.94
Inverters/Circuit
12
17
kW/Circuit (based on 270W modules)
3.24
4.59
If I have a 100A residential panel with a 100A main, I am limited to backfeeding a single 20A circuit or doing a supply side connection. If I got 1500kWh/kW with ABB and 1450 kWh/kW (3% energy loss due to clipping) with Enphase, would it be worth avoiding the supply side connection? What if I get 1472 kWh/kW? Where would you draw the line.
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf
Sent: Monday, August 25, 2014 11:11 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Inverters Maximum Input Ratings
Look, guys, what’s beyond dispute is that when we size the solar array higher than the nameplate inverter output, there will be clipping that takes place….i.e., harvestable solar power that goes nowhere. The higher that oversize percentage, the more clipping will take place.
If the design choice, as noted below, is to use a 270-watt module (from a manufacturer that learned last week that a recall notice was published by the U.S. Consumer Product Safety Commission https://www.cpsc.gov/en/Recalls/2014/SolarWorld-Recalls-Solar-Systems-with-Copper-Grounding-Lugs/ ), does it make sense to use a micro inverter that has a max output of about 225 watts (M215) or 250 watts (M250) when there are micros (e.g., ABB 300) that can handle the full output of the 270 which guarantees NO clipping?
marco
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jerry Shafer
Sent: Monday, August 25, 2014 8:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Inverters Maximum Input Ratings
Why dont you use the m250 anyway as the 250's so far are more reliable then the 215 have been. A little off topic i know.
On Aug 25, 2014 1:41 PM, "Jason Szumlanski" <jason at fafcosolar.com<mailto:jason at fafcosolar.com>> wrote:
I had a tough customer recently that grilled me on how we can put a 270W solar module on a 215W inverter. Fortunately, Enphase has a wonderful white paper on the subject. However, it got me thinking... Enphase has demonstrated that higher output panels in many climates (hot SW Florida included) can benefit from modules that far exceed the inverter rating, and even exceed the inverter's "recommended input" rating. Enphase has shown that 270W+ modules can show energy harvest on the M215 where it makes sense to "oversize" the module.
I also received a similar query from a rather uninformed plan reviewer in an area AHJ along similar lines. Fortunately I was within the "recommended input" rating on the spec sheet of 270W with a 265W module, but I wonder what would happen if I had paired the M215 with a 280W module on my plans, which are becoming readily available now in 60 cell modules with 300W modules on the near horizon. I'm pretty sure my plan would have been kicked back for exceeding the manufacturer's recommendation.
My question, which applies to string inverters and microinverters, is how much is too much, what would happen if you paired an array that far exceeded the rating, and how do inverter manufacturers determine the recommended and/or maximum rating of the connected module or array? Also, why do some manufacturers have a simple recommendation while others have a "maximum" rating?
Jason Szumlanski
Fafco Solar
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140826/074d0445/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 332 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140826/074d0445/attachment.jpg>
More information about the RE-Wrenches
mailing list