I have checked out the Midnite purpose-made BOS cabinets for Sunny Island inverters.  My problem is they must be co-located with the inverters.  The OCPD needs to be closer to the batteries than this usually allows.  If your inverters are mounted on an interior wall with the batteries directly on the other side, these may work out OK because your battery leads will be short.

 

I forget if the Midnite panels have AC distribution.  I have divorced myself from using any sort of AC distribution built by RE manufacturers.  I am weary of making custom leads for QOU breakers and trying shoehorn too much into an FX1000,  Radian or Midnite BOS cabinet, for example.  We use only off-the-shelf load centers.  They are a good value due to economy of scale.  We provide one each for inverter fed, generator fed and mini-grid or grid fed, if present.  Bypassing can be done easily with factory or custom made interlocks.  (I know custom made interlocks are not listed hardware but I can’t seem to find fault with such a simple device.)

 

See the following link for some details on how this can be done.  By the way, if you are transferring more than 100 amps you really need to use commercial grade panels.  We see the main lugs used as a house feeder but this has always bothered me.

 

http://www.millersolar.com/MillerSolar/Portfolio/Commercial/Red_Mountain/Red_Mountain.html

 

William Miller

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Monday, August 25, 2014 4:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island battery cable setup

 

Also see all of Midnite Solar products. The SMA epanels are functional but expensive. You may also like their battery combiner. Its good for 1000A DC.

Outback FX1000

William

Miller Solar

> On Aug 25, 2014, at 10:43 AM, Darren Anderson <darren at self.org> wrote:
>
> Hi All ­ just wondering what products or general setup others are using to
> split the battery cables to two or more Sunny Islands?
> _________________________
> Darren Anderson | Project Manager
> Solar Electric Light Fund



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140825/b3bb325a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140825/b3bb325a/attachment.jpg>


More information about the RE-Wrenches mailing list