[RE-wrenches] Batteries in a dwelling - Venting Concorde AGMs

Drake drake.chamberlin at redwoodalliance.org
Tue Jul 29 12:00:49 EDT 2014


This is a reply to a post by Alan from June 21st. I'm replying 
because I've had to deal with this issue also. It seems to me that 
the 2014 NEC Handbook is fairly clear that we are not required to 
vent any batteries to the outside.

"480.9 Battery Locations
Battery locations shall conform to 480.9(A), (B), and (C).
(A) Ventilation. Provisions appropriate to the battery technology
shall be made for sufficient diffusion and ventilation of gases
from the battery, if present, to prevent the accumulation of an
explosive mixture.
Ventilation is necessary to prevent classification of a battery location
as a hazardous (classified) location, in accordance with
Article 500.
Mechanical ventilation is not mandated. Hydrogen disperses
rapidly and requires little air movement to prevent accumulation.
Unrestricted natural air movement in the vicinity of the battery,
together with normal air changes for occupied spaces or heat
removal, normally is sufficient. If the space is confined, mechanical
ventilation may be required in the vicinity of the battery.
Hydrogen is lighter than air and tends to concentrate at ceiling
level, so some form of ventilation should be provided at the
upper portion of the structure. Ventilation can be a fan, roof ridge
vent, or louvered area.
Although valve-regulated batteries are often referred to as
"sealed," they actually emit very small quantities of hydrogen gas
under normal operation and are capable of liberating large quantities
of explosive gases if overcharged. These batteries therefore
require the same amount of ventilation as their vented
counterparts."

I think that the confusion come is with the statement "These 
batteries therefore
require the same amount of ventilation as their vented
counterparts."

As we see from the statement "Unrestricted natural air movement in 
the vicinity of the battery,
together with normal air changes for occupied spaces or heat
removal, normally is sufficient," the concern is with explosive 
gasses being restricted to a small area, where explosive 
concentrations of hydrogen can build up.

The article also has the statement "Provisions appropriate to the 
battery technology" which should be taken into account. In practice, 
liquid electrolyte batteries stink and emit toxic fumes, so we do 
vent these outside.

It does sound like different voices have worked their way into this 
code section, which can open the way to various interpretations. But, 
if you look at the photos in the NEC Handbook of batteries, they are 
on unenclosed racks inside of a building.

Drake




At 12:06 AM 6/22/2014, you wrote:
>Bob,
>We had a case in February in which an AHJ insisted that we vent a 
>Midnite cabinet with a dozen 2V 9150T batteries. We fought it all 
>the way to the state Technical Advisory Committee, the top arbiter 
>of Code issues. We fought to a draw: we finally agreed to put in the 
>vent to get our final passed, and the committee permanently tabled 
>the issue so there is no precedent set. To continue to fight this 
>would have required bringing in professional engineers, as some of 
>the committee members were reluctant to make their own decisions 
>about the issue and wanted to pass the buck. As I recall, the Zephyr 
>Power Vent was ultimately never hooked up to the Classic 
>controller's auxiliary, as the necessary work was handled by the GC 
>(rather than by us) at a quite remote location. The challenge to the 
>AHJ was a pain in the butt, although we were paid by the clients for 
>the effort, as they agreed with the absurdity of the inspector's demand.
>
>I have attached a few documents I gathered and prepared in this 
>case. You do not need to vent AGMs if the larger space in which the 
>battery enclosure is located has a typical and normal amount of 
>natural air circulation and convective air exchange. Also, you can't 
>duplicate what Kevin describes below with a vented enclosure - 
>Kevin's approach requires a "sealed and vented battery enclosure". 
>By design, your enclosure is unsealed.
>
>Putting in vents "for the next guy" also makes no sense. If you 
>install 8 flooded L16s on two shelves in a Midnite MNBE-Cl16 
>enclosure, you won't be able to routinely add water to the cells. 
>The cabinet was designed and built for VRLA batteries. So any 
>venting you install now would have to be redone to fit a cabinet 
>built for flooded batteries with top access.
>Allan
>
>Allan Sindelar
><mailto:allan at sindelarsolar.com>allan at sindelarsolar.com
>NABCEP Certified PV Installation Professional
>NABCEP Certified Technical Sales Professional
>New Mexico EE98J Journeyman Electrician
>Founder (Retired), Positive Energy, Inc.
>505 780-2738 cell
>
>
>On 6/21/2014 1:30 PM, Bob Clark wrote:
>>RE-Wrenches:
>>
>>2014 NEC 480.9 (A) has two informational notes that seem to point 
>>to the possibility of not having to vent AGMs.
>>
>>Here is what I was going to do with 8 Concorde SunXtender 
>>Batteries, 6V, 405Ah, L16, PVX-4050HT:
>>
>>1.  Put them in a Midnite Solar, MNBE-CL16 Battery Enclosure (which 
>>is not a sealed box) in a "battery closet."
>>2.  Vent the box out of the top of the box and through the wall of 
>>the house with pipes like Kevin Pegg suggests.
>>
>>Do any of you see any problems with this?  Venting unnecessary?
>>
>>One consideration is the "next guy" who occupies this house may 
>>want flooded batteries, in which case, the vent system would 
>>definitely be necessary.
>>
>>Bob Clark
>><mailto:bclark at solar-wind.us>bclark at solar-wind.us
>>
>>
>>
>>On Apr 4, 2014, at 2:49 PM, Kevin Pegg 
>><<mailto:kpegg at energyalternatives.ca>kpegg at energyalternatives.ca> wrote:
>>
>>>Hi William,
>>>
>>>In the cold north here in Canada, this is the most common way we 
>>>install batteries - within the heated envelope of a home or shop, 
>>>installed in a sealed & vented battery enclosure.
>>>
>>>Hydrogen is easy to vent as it is lighter than air. We use a 
>>>process similar to below. I see a lot of installations with power 
>>>vents that are not done properly - exhaust only but no intake as 
>>>example. They can also fail. Or installed in such a way that 
>>>outside wind influences could actually reverse the flow and 
>>>pressurize the battery box! Air flow needs to be balanced.
>>>
>>><http://www.bdbatteries.com/hydrogenventing.php>http://www.bdbatteries.com/hydrogenventing.php
>>>To remove the thermal air currents present in a battery box 
>>>venting system, you must create a natural heat sink between the 
>>>vent tubes to neutralize the difference in temperature. This in 
>>>turn will stagnate the air, allowing the hydrogen which is lighter 
>>>than air, to rise and escape the battery box. Make sure the 
>>>smaller tube, the one inside, extends to the bottom of the box. 
>>>This will allow "heavier" fresh air to fall to the floor of the 
>>>box and retard hydrogen entry. The intake for the hydrogen is at 
>>>the top of the box, the exterior tube in the system. Hydrogen will 
>>>travel in the opposite direction through the larger outer pipe as 
>>>it is lighter than the air surrounding it. Several good methods 
>>>for constructing this vent system exist, we particularly like to 
>>>see 1/2 inch copper pipes inside 1 inch pipe. Any highly 
>>>conductive metal pipe will work it will transfer heat quickly. 
>>>Galvanized, steel, and other pipes that spark when rubbed aren't 
>>>as great. DO NOT USE THESE IN EARTHQUAKE ZONES.
>>>
>>>DO NOT USE PVC FOR THIS VENT SYSTEM....PVC DOES NOT CONDUCT HEAT 
>>>WELL ENOUGH! Copper, aluminum, and other non sparking conductive 
>>>metals are great!
>>><Outlook.bmp>
>>>
>>><Outlook.bmp>
>>>-----Original Message-----
>>>From: 
>>><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org 
>>>[mailto:re-wrenches-bounces at lists.re-wrenches.org]On Behalf Of 
>>><mailto:william at millersolar.com>william at millersolar.com
>>>Sent: April 4, 2014 9:29 AM
>>>To: RE-wrenches
>>>Subject: [RE-wrenches] Batteries in a dwelling
>>>
>>>Friends:
>>>
>>>I am proposing installation of vented batteries in a first floor 
>>>garage of a dwelling.  The dwelling areas are on the second 
>>>floor.  I am nervous about the cohabitation of batteries and humans.
>>>
>>>I reviewed the NEC and could not find any prohibition.  Do any of 
>>>you have any advice on how this is accomplished in the mot safe manor?
>>>
>>>I presume good ventilation and an otherwise sealed room are 
>>>advised.  I will propose additional smoke detectors, locked doors 
>>>and I will research hydrogen detectors.  A good spill kit and all 
>>>PPE will be staged as usual.
>>>
>>>Thanks in advance for the forthcoming, always expert advice.
>>>
>>>William Miller
>>>
>>>
>>>_______________________________________________
>>>List sponsored by Home Power magazine
>>>
>>>List Address: 
>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>
>>>Change email address & settings:
>>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive: 
>>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>List rules & etiquette:
>>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out participant bios:
>>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140729/d1d783c1/attachment.htm>


More information about the RE-Wrenches mailing list