[RE-wrenches] Sunny Island retrofit
Brian Teitelbaum
bteitelbaum at aeesolar.com
Sun Jul 6 14:59:53 EDT 2014
Thanks boB and Robin. Good explanation.
I wish that SMA would be more clear on this in the manuals. It shouldn’t be
that hard.
Do other inverters with built-in transfer relays also self-protect against
over-current? I’ve never wanted to try my luck.
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *boB at midnitesolar.com
*Sent:* Friday, July 04, 2014 2:14 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Sunny Island retrofit
I'll let Robin weigh in here as well...
Brian, It used to be very clear on the older 5048 Sunny Island. They wanted
a 70 amp breaker connected to the input. They were assuming a thermal
breaker. 70 times .8 = 56. We use hydraulic/magnetic breakers. They only go
up to 60 amps and can be ran at full current continuously. You cannot feed
a 56 amp circuit with less than a 56 amp breaker, so 60 works just fine.
The Sunny Island does shut down above 56 amps. SMA is not counting on a
breaker to keep from breaking the inverter. That would never work. The
breaker is there to protect the wiring, not the relay or anything else in
the inverter.
Thanks,
Robin
On 7/4/2014 11:30 AM, Brian Teitelbaum wrote:
Thanks for the clarification boB.
I would still however like to get confirmation from that the Sunny Island
does indeed protect itself from AC current over 56A. It says nothing to
this effect in the literature (at least that I can find), and would seem to
contradict the “Higher input currents must not be connected to the Sunny
Island” that it actually does say.
Steve, if you see this, could you please confirm the automated AC current
protection circuitry?
If we don’t get a reply from Steve on this list, I’ll contact him directly
and post his reply here, although it might be after the Intersolar show
next week.
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *boB at midnitesolar.com
*Sent:* Friday, July 04, 2014 11:11 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Sunny Island retrofit
The Sunny Island has circuitry to protect itself over 56 amps. I think it
shuts off.
The 60 amp circuit breaker is there to protect the wiring. Customers
complain when they cannot
get the full 56 amps from the system and 50 amps is the next nominal
current breaker below 60 A.
Thanks,
boB
On 7/3/2014 11:09 PM, Brian Teitelbaum wrote:
Yes it is. But since you have to install inverters based on the
manufacturer’s requirements, SMA’s instructions trump MidNite’s, IMHO.
Since MidNite and SMA worked jointly together to develop those E-Panels, I
can only assume that either it’s an oversight on both of their parts, or
that SMA is being very conservative on the switch rating in their
installation manual and “Technical Description”, where that line I quoted
is repeated. This wouldn’t surprise me, but if so SMA needs to issue a
correction.
Maybe boB at MidNite or Steve from SMA will pipe in with some info…
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Ray Walters
*Sent:* Thursday, July 03, 2014 10:18 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Sunny Island retrofit
A 60 amp continuously rated AC breaker is what is actually being used in
the UL listed E Panel from Midnite.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 7/3/2014 9:01 PM, Brian Teitelbaum wrote:
Mac,
Be careful with breaker sizing here. The transfer switch in the SMA SI5048
is only rated for 56A at 120 VAC. From the SI manual:
“The maximum input current allowed on the Sunny Island is 56 A. Higher
input currents must not be connected to the Sunny Island.”
To protect that switch properly, you would need to use a 50A breaker
(unless you can find a 55A breaker that fits in your AC panel). Since most
common AC breakers are only rated for 80% duty, you would need to limit
that 50A breaker to a continuous 40A load. That’s more than the max output
current of the Fronius 10.0-1, although it’s debatable that the output of a
PV inverter is “continuous”. It certainly could be in some situations,
especially with a tracker mount, although even with a fixed array, you
could see max rated output for at least a couple of hours per day.
I agree with the suggestion of putting part of the PV array on a 5kW Sunny
Boy, or adding a second Sunny Island and using two Sunny Boy 5000’s. Using
two Islands would eliminate the need for a transformer, and allow for full
array power during grid outages.
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Mac Lewis
*Sent:* Thursday, July 03, 2014 9:34 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Sunny Island retrofit
Hi Wrenches,
Jerry, I think you are correct, sma gear all around would be best. This
will be my recommendation but I am sensitive to this substantial cost.
Dave, if I add the second Sunny Island, I don't think I will be throttled
back because the transfer relays are rated for 60A. This should pass the
full current of the output of the Fronius, which is 41.7A. My concern is
more during backup mode, if the Sunny Islands could "trick" the Fronius
into staying on line. I would add either load dump relay control or an AC
interrupt relay to knock the Fronius off-line if the batteries were full,
in addition to the frequency shift control that the Sunny Island offers.
Thanks for the input, I'll shoot for all SMA gear.
Thanks
On Thu, Jul 3, 2014 at 9:23 AM, Dave Click <daveclick at fsec.ucf.edu> wrote:
Mac, that Island interconnects with a max 70A 1P breaker (6.7kW
continuous), so unless they have a constant critical load draw or the
Fronius is massively oversized, you probably don't want to AC couple the
Fronius. The 5048 is also able to output a continuous 5000W only when it's
cooler than 77F and it derates above that (4500W at 95F, for example). I
don't believe its surge ratings apply to the AC2 output back into the
utility but they probably wouldn't be enough, anyway. I think that whenever
the Fronius output reached about 6000W, the SI would shift its frequency to
switch the Fronius off. Cheapest may be along the lines of your first
option-- not sure what the PV stringing is like but maybe you could move a
string or two off the Fronius and put it onto a new Sunny Boy with an
autoformer. Since I imagine this system doesn't have PV WIRE on the module
leads or home runs, officially I'd recommend a classic Sunny Boy. Then
leave the Fronius as-is.
Unless of course the customer thought they were buying a system with the
full 10kW supplying critical loads when the utility is down... then the
original contractor is stuck with buying the second SI they should have
installed in the first place.
DKC
On 2014/7/3, 10:46, Mac Lewis wrote:
Hello wrenches,
I wanted to run this scenario by the forum. I have spoken with SMA about
this, but want some other opinions.
We were recently contracted by a fellow solar company to do some warranty
work for them out of town on a Sunny Island system that they had installed
about 5 years ago. It was VERY poorly implemented originally and was never
installed as SMA intended. In fact, during a small power outage, the only
loads that never came back on after the utility was back on line were the
loads in the critical load panel. Oops.
Anyway, our job is to get it working properly for the least amount of cost
possible. They have a Fronius IG Plus 10.0 fed into a 400A service panel.
The Sunny Island 5048 AC Input also comes off of this panel and feeding a
120V only critical load panel. Please note that there is no solar fed into
the AC output side of the Sunny Island, because there is not 120/240
available and thus there is no possible way for this system to utilize the
solar while the grid is not present.
I see two options (but there may be more): pull out Fronius, put in Sunny
Boy inverters and an autoformer, wire properly. Another option is to add
second Sunny Island and try to AC couple the Fronius with the two Sunny
Islands. The second option is less expensive overall, but I'm hesitant to
rely on AC coupling with the Fronius.
I'd appreciate any thoughts on this.
Thanks
Mac Lewis
"Yo solo sé que no sé nada." *-Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140706/91a95711/attachment.htm>
More information about the RE-Wrenches
mailing list