[RE-wrenches] Magnum and Pumps

dave at independentpowerllc.com dave at independentpowerllc.com
Thu Jul 3 01:56:14 EDT 2014


Bob,
Very good performance. Able to take a high charge rate and likes higher voltages than most other VRLA's (up to 7.5v for 6v). Only negatives I see are: not md in USA and very expensive.
Dave Palumbo
--
Sent from myMail app for Android
Wednesday, 02 July 2014, 11:58PM +02:00 from "RE Ellison" <reellison at gmail.com>:
What has been everybody’s experience with Full River Batteries?
 
Bob
 
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]  On Behalf Of  Roy Butler
Sent: Wednesday, July 02, 2014 3:12 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Magnum and Pumps
 
Sweet....thanks for that info, I stand corrected!
Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
IREC Certified Master Trainer™ for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com
 
Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
www.smallwindconference.com
 
Although no trees were killed in the sending of this message,
a large number of electrons were terribly inconvenienced.
 
               
On 7/2/2014 2:55 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
>Hi Roy,
> 
>The FullRiver DC400-6 AGM battery can issue 2000 amps for 5 seconds so he should be fine.
> 
>Larry
>On Jul 2, 2014, at 12:35 PM, Roy Butler < roy at four-winds-energy.com > wrote:
> 
>I haven't seen anyone mention the battery bank. If I understand correctly, there's a single string of sealed
>L16 batteries on this inverter. I have my doubts as to whether or not that bank can provide the high current
>the inverter needs to start this load.
>
>Roy Butler
>NABCEP Certified Solar PV Installer®
>NYSERDA eligible PV & wind installer
>IREC Certified Master Trainer™ for Small Wind Installer
>Four Winds Renewable Energy, LLC
>8902 Route 46, Arkport, NY 14807
>607-324-9747  www.four-winds-energy.com
> 
>Join us at the 10th Annual Small Wind Conference
>A Gathering of Installers, Manufacturers, Dealers, & Distributors
>June 17 and 18, 2014 in Stevens Point, Wisconsin
>www.smallwindconference.com
> 
>Although no trees were killed in the sending of this message,
>a large number of electrons were terribly inconvenienced.
> 
>               
>On 7/2/2014 2:10 PM, Jason Szumlanski wrote:
>>To further qualify my statements, the inverter will start the pump without issue, but I should echo the warnings by others that if there are other loads present, especially other motor loads that could start  ​ concurrently, you may experience issues. As long as your customer understands the limitations and possibilities, you may be just fine.
>> 
>>Jason Szumlanski
>>​ Fafco Solar ​
>> 
>> 
>>On Wed, Jul 2, 2014 at 11:00 AM, Jason Szumlanski < jason at fafcosolar.com > wrote:
>>For what it's worth, I've run a single speed 1.5HP pool pump with a MS4448PAE in a mobile application on a 38.4kWh battery bank (sixteen Rolls S-530's). I have also run a 2.5HP Hayward EcoStar Variable Speed pool pump at full RPM, but that startup current is likely less than you well pump.
>> 
>>I'm going to guess your 3/4HP well pump will be a breeze to start with this inverter.
>> 
>>Jason Szumlanski 
>>​ Fafco Solar ​
>> 
>> 
>>On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar < allan at sindelarsolar.com > wrote:
>>Drake,
>>As a normal CYA, I'll always gently let a customer know that this (or any) particular combination of inverter and load sometimes proves incompatible, just in case the unexpected happens. (We once had a MS4448 that would not reliably start and run a condensing boiler; a switch to a different boiler resolved the issue.)
>>
>>Having said that note of caution, I wouldn't give it any concern. 3/4 HP and 1 HP well pumps have never been an issue; I would expect 1.5 HP to be easy to run. At 2 HP I'd be asking these questions here.
>>
>>You might check that it's a 3-wire, capacitor-start motor, but nowadays nearly all are. Two-wire pumps (with no control box) can add 50% to the surge.
>>
>>The Magnum has a fairly poor voltage regulation response. Sometimes the AC voltage can drop to ~80 VAC momentarily. So you might also caution your customer that the lights may flicker when the pump starts. In our home we know whenever our Kenmore fridge turns on.
>>
>>Allan
>>Allan Sindelar
>>allan at sindelarsolar.com
>>NABCEP Certified PV Installation Professional
>>NABCEP Certified Technical Sales Professional
>>New Mexico EE98J Journeyman Electrician
>>Founder (Retired), Positive Energy, Inc.
>>505 780-2738 cell
>> 
>>On 7/2/2014 8:17 AM, Drake wrote:
>>>Hello Wrenches,
>>>
>>>We are hoping to use a Magnum PAE 4448 to back up a household that includes a 3/4 HP deep well pump. There is about 120 feet of vertical rise and about 1000 feet of horizontal distance.
>>>
>>>I have been told that there is a correlation between the locked rotor current of a pump and the predictable ability of a specified inverter to power that pump.
>>>
>>>The plumber who installed the pump left no paperwork and retained no records of what pump he put in the hole last year. He could only say it was a 3/4 HP pump. We are therefore unable to obtain the manufacturer's nameplate specifications.
>>>
>>>The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100 MS surge of 40 A. According to the NEC Table 430.251(A), a 3/4 HP motor has a locked rotor current of 41.4 amps at 230 V.
>>>
>>>This inverter can surge at 35.4 A for 5 seconds. The specified battery bank will be 8 Full River  L-16 AGMs. Can anyone say if:
>>>*  Is there enough information to know if this setup will handle the pump, and if so, will it?
>>>*  How can an inverter's ability to power a motor or pump be calculated by knowing its locked rotor current? Which surge periods should be compared to the locked rotor current?
>>>*  Does the surge current need to equal locked rotor. How long must the inverter meet its required maximum surge?
>>>*  From experience with Magnums and pumps, does this seem like a good combination?
>>>
>>>Thank you,
>>>
>>>Drake
>>>
>>>Drake Chamberlin
>>>Athens Electric LLC
>>>OH License 44810
>>>CO License 3773
>>>NABCEP Certified Solar PV
>>>740-448-7328
>>>http://athens-electric.com/  
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>> 
>>List Address: RE-wrenches at lists.re-wrenches.org
>> 
>>Change listserver email address & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>>List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>> 
>>Check out or update participant bios:
>>www.members.re-wrenches.org
>> 
> 
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address:  RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:  http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
> 
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
> 
>List Address: RE-wrenches at lists.re-wrenches.org
> 
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
> 
>Check out or update participant bios:
>www.members.re-wrenches.org
> 
 
----------------------------------------------------------------------
No virus found in this message.
Checked by AVG -  www.avg.com
Version: 2014.0.4592 / Virus Database: 3986/7776 - Release Date: 07/01/14
----------------------------------------------------------------------
No virus found in this message.
Checked by AVG -  www.avg.com
Version: 2014.0.4592 / Virus Database: 3986/7776 - Release Date: 07/01/14
_______________________________________________
List sponsored by Redwood Alliance
List Address:  RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:  http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140703/a6c1c39c/attachment.htm>


More information about the RE-Wrenches mailing list