[RE-wrenches] Pv wire
Bill Brooks
billbrooks7 at yahoo.com
Fri Jun 27 20:20:37 EDT 2014
Kirk,
The tables in Appendix C are just for reference. They are not part of the Code. The only real part of the code is in chapter 9:
Table 1 Percent of Cross Section of Conduit and Tubing for
Conductors and Cables
Number of Conductors and/or Cables Cross-Sectional Area (%)
1 53
2 31
Over 2 40
Many conductors do not have standard cross-sectional areas.
Bill.
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Thursday, June 26, 2014 11:13 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pv wire
Yeah, 1k/2k wire shows a diameter of 0.26" on the spec sheet, or 0.053093 in^2.
Jason Szumlanski
Fafco Solar
<https://wisestamp.appspot.com/pixview.gif?p=chrome&v=3.42.0&t=1403806149111&u=dedcb4cd140ce271>
<http://ws-stats.appspot.com/ga/pixel.png?yes__count=true&e=legacy_impression>
On Thu, Jun 26, 2014 at 2:06 PM, Kirk <kirk at vtsolar.com <mailto:kirk at vtsolar.com> > wrote:
Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv wire is thicker.
Kirk Herander
VSE
On Jun 26, 2014, at 1:49 PM, Jason Szumlanski <jason at fafcosolar.com <mailto:jason at fafcosolar.com> > wrote:
I use this site when I need a quick answer. Use RHH (covered) with one conductor. You get the same answer.
http://www.electrician2.com/calculators/rf_calculator.html
Jason Szumlanski
Fafco Solar
On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski <jason at fafcosolar.com <mailto:jason at fafcosolar.com> > wrote:
0.0437435 per this attached spec sheet for 600V.
Jason Szumlanski
<http://ws-stats.appspot.com/ga/pixel.png?yes__count=true+&e=legacy_impression>
On Thu, Jun 26, 2014 at 1:15 PM, Kirk <kirk at vtsolar.com <mailto:kirk at vtsolar.com> > wrote:
Hi folks,
What is the proper approximate in2 area to use for #10 1kva/2kva pv wire for calculating conduit fill? I'm on a job site and don't have the specs with me. Thanks.
Kirk Herander
VSE
___
---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140627/1f3c3dce/attachment.htm>
More information about the RE-Wrenches
mailing list