[RE-wrenches] Combining Multiple Inverters

Corey Shalanski cshalanski at joule-energy.com
Thu Jun 26 18:11:57 EDT 2014


ᐧ
We considered the necessity to shut down individual inverters and
determined that the added costs of an inverter output combiner panel were
not merited. I agree that in theory it seems beneficial to be able to
switch each inverter individually, but how often does this occur in
practice? For the relatively infrequent cases where we need to return to a
jobsite and shut down an inverter - for troubleshooting/removal/etc. - we
do not mind shutting down the other inverters (up to a limit) for what is
hopefully a short period of time.

Again, this whole line of reasoning may be shown to be faulty if someone
can directly point to the Code section that requires OCPD on each
individual inverter.

--
Corey


On Thu, Jun 26, 2014 at 9:20 AM, <re-wrenches-request at lists.re-wrenches.org>
 wrote:

>
> Message: 5
> Date: Wed, 25 Jun 2014 19:17:57 -0700
> From: William Miller <william at millersolar.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Combining Multiple Inverters
> Message-ID: <04F4B8FD-E280-4BF2-B5A4-C2FCA8D1C7A6 at millersolar.com>
> Content-Type: text/plain; charset="utf-8"
>
> Not allowed. You need a dedicated OCPD. Plus seems like a really bad idea.
>  How do you shut down just one inverter?
>
>
>