Code requires OCPD on the output of each inverter, so not sure where the savings would be..
-----Original Message-----
From: "Corey Shalanski" <cshalanski at joule-energy.com>
Sent: 6/25/2014 21:19
To: "RE-wrenches at lists.re-wrenches.org" <RE-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Combining Multiple Inverters
I am curious about best practices for combining the output of multiple
inverters:
- We are considering using an insulated tap "Polaris/Burndy" connector
in lieu of a solar accumulation panel. We would then run the output of this
tap connector through a fused disconnect and on to the interconnection.
Does anyone else do this?
- In the above scenario, how should we size the wire between each
inverter's output and the tap connector? Since there is no OCPD on this
wire, would we have to use the same wire gauge as the combined output? or
can we get away with sizing each wire according to its associated inverter
output rating?
--