[RE-wrenches] AFCI disturbances.
Jerry Shafer
jerrysgarage01 at gmail.com
Tue Jun 24 13:17:27 EDT 2014
we will never use wire nuts I have seen to many issues we will use
insulated cable connector blocks or if there is room splicer blocks, I have
been updating inverters with no problems if its a larger inverter more then
2 strings we use 1000 volt PV wire and the combiner box. the new inverters
require some additional hardware to be compliant
Jerry
On Tue, Jun 24, 2014 at 9:35 AM, William Miller <william at millersolar.com>
wrote:
> Steve:
>
> The PV is 200 feet away on the other side of a building. We have THWN in
> PVC conduit. This job was installed over 10 years ago. We don't want to
> repull all of the leads for 6 strings in PV wire.
>
> We Void splices like the plague but the PV leads terminated in a HU361
> switch and we needed to splice on some short leads to make this work.
>
> Are you telling me we can no longer use 600 volt rated building wire
> and/or standard 600 volt rated wire nuts on PV circuits with your products?
> If so, this is a BIG deal for installers.
>
> Thanks,
>
> William
>
> Miller Solar
>
> > On Jun 24, 2014, at 8:52 AM, Steve Jefferson <
> Steve.Jefferson at sma-america.com> wrote:
> >
> > Morning William,
> >
> > You can contact me offline, or better yet, call our Service Line. I
> checked and see no calls in about AFCI issues.
> >
> > Also, we don't recommend wire nuts on DC conductors (or AC) due to the
> probability of unreliable and highly resistive connection.
> >
> > Thanks
> >
> > SMA America, LLC
> > Steve Jefferson
> > Service Line Supervisor
> > 3925 Atherton Ave
> > Rocklin, CA 95765 - 3714
> > U.S.A.
> > Tel: +1 916 625 3185 (direct)
> > Fax: +1 916 625 0871
> > Mobile: +1 916 622 4253
> > Email: Steve.jefferson at SMA-America.com
> > www.SMA-America.com
> >
> >
> >
> > This email and any attachments thereto may contain SMA America, LLC
> confidential, privileged and private material for the sole use of the
> intended recipient. Any review, copying, or distribution of this email (or
> any attachments thereto) by others is strictly prohibited. If you are not
> the intended recipient, please contact the sender immediately and
> permanently delete the original and any copies of this email and any
> attachments thereto. Thank you.
> >
> >
> >
> > -----Original Message-----
> > From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of William Miller
> > Sent: Monday, June 23, 2014 3:40 PM
> > To: RE-wrenches
> > Subject: [RE-wrenches] AFCI disturbances.
> >
> > Friends:
> >
> > We are starting to replace dying SB2500s with new units. The AFCI is
> giving us fits with disturbances. We are told we can not even use wire nuts.
> >
> > Has anyone else dealt with this? What have you learned?
> >
> > Thanks in advance.
> >
> > William
> >
> > Miller Solar
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140624/f4ebafba/attachment.htm>
More information about the RE-Wrenches
mailing list