[RE-wrenches] SI6048s won't charge from generator

william at millersolar.com william at millersolar.com
Wed May 7 00:59:35 EDT 2014


Friends:

 

Here is the update on this problem, in case anyone needs to know in the
future:

 

We reluctantly left the generator running all weekend,  Monday morning we
fired the system up again.  We had swapped which inverter was Master on
Friday, so Monday we swapped back to the preferred Master and re-ran the
quick configuration.  Inexplicably, the system immediately connected to the
generator and began charging.  We still don't know what caused the problem.

 

It must not have been the fact we started the generator from the generator
control.  It must not have been the extra neutral connected between the Gen
Fed panel and the Main panel for bypass.  It would have been unfortunate if
the cause of the problem had been either scenario because we need these two
functions:  1. to be able to start the generator from the generator control
and, 2. we must have bypass capabilities.

 

SMA tech support is reviewing the history log to see if they can figure this
out.  If I learn more, I will let you know.  I always assume that someday
someone may have the same problems I have had so I want the searchable
record to be complete.

 

Thanks for the help.

 

William Miller

 

 

 

Gradient Cap_mini
Lic 773985
 <http://www.millersolar.com/> millersolar.com
805-438-5600

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of
william at millersolar.com
Sent: Saturday, May 03, 2014 1:08 PM
To: RE-wrenches
Subject: [RE-wrenches] SI6048s won't charge from generator

 

Friends:

 

We commissioned a new SI6048 3 phase system yesterday.  It will create power
but it won't charge from the generator.  This is a generator that was
working with a 3 SI4548 system.  We checked rotation and volts and hertz.
We checked inverter programming.  All seems correct.  There is no phone
service so using tech support is cumbersome.

 

Has anyone experienced this problem before?

 

Thanks!

 

William

 

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140506/09f82a74/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140506/09f82a74/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140506/09f82a74/attachment-0003.jpg>


More information about the RE-Wrenches mailing list