[RE-wrenches] Stainless NEMA4x load center

Kirpal Khalsa solarworks at gmail.com
Wed Apr 23 11:46:22 EDT 2014


Jason...thanks...I just got off the phone with SolaDeck.....I think that
will work perfectly.....I guess this is a relatively new item for them.  it
was not on their web site but they gave me all the part numbers to order
via the distributor....
Thank you!!


Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-299-0402 o


On Wed, Apr 23, 2014 at 8:36 AM, Jason Szumlanski <jason at fafcosolar.com>wrote:

> See my other response, but you should definitely consider SolaDeck in this
> case. You want SolaDeck Model 0786-41. Make sure you order the correct
> breakers, bus bars, and Neutral terminal block.
>
>
> http://www.rstcenterprises.com/soladeck/products/1741_combiner_enclosure.phtml
>
> ​The attached picture is the Soladeck on my 3-string ​Enphase system at
> home (note: neutral block was not on DIN rail yet). There are four neutrals
> on the bottom of the N block because I center-fed one inverter string, so I
> had four sets of Enphase cable coming into the box, which is admittedly a
> little tight. If you need to do this, I recommend transitioning to THWN in
> a separate combiner and just bringing in three strings through one or two
> conduits.
>
>
> ​[image: Inline image 1]​
>
>
> Jason Szumlanski
>
> ​Fafco Solar​
>
>
>
>
> On Wed, Apr 23, 2014 at 11:17 AM, Kirpal Khalsa <solarworks at gmail.com>wrote:
>
>> Drake.....we want it to mount flush to the slope of a sloped roof....The
>> NEMA 3R are supposed to be mounted vertically....This is for a large
>> residential Enphase system and we wanted to combine the circuits on the
>> roof and bring one set of conductors down.....
>> I did find one custom made by Eaton(Cutler Hammer), but....$952 my cost
>> is too much..I have had them make me one out of fiberglass in the past but
>> it is about 3 years into its roof mount life and showing signs of UV
>> degradation...looking for other options....I think i will dig a little
>> deeper at Midnite Solar.....They may have something....Theirs and Outback's
>> PV combiners are rated to be mounted at a slope....i think it is down to 14
>> degrees pitch (3/12)
>> Thanks.
>>
>> Sunny Regards,
>> Kirpal Khalsa
>> NABCEP Certified PV Installation Professional
>> Renewable Energy Systems
>> www.oregonsolarworks.com
>> 541-218-0201 m
>> 541-299-0402 o
>>
>>
>> On Wed, Apr 23, 2014 at 8:11 AM, Drake <
>> drake.chamberlin at redwoodalliance.org> wrote:
>>
>>>  That would be a nice piece of hardware. Is there any reason you can't
>>> use a NEMA 3R panel?  They are used on roofs quite a bit, and are readily
>>> available.  The Square D, 8 space, outdoor box should work in most rooftop
>>> environments for the purpose you describe.
>>>
>>> At 06:18 PM 4/21/2014, you wrote:
>>>
>>> Hello Friends!
>>> Anyone have a lead for* NEMA 4x* stainless load centers (electrical
>>> panel)? Â Looking for 4 circuit version rated at about 60-100A @ 240VAC.
>>>
>>> Would like to use it for rooftop combiner for 3 Enphase inverter output
>>> circuits.
>>> Thank you!!
>>>
>>> Sunny Regards,
>>> Kirpal Khalsa
>>> NABCEP Certified PV Installation Professional
>>> Renewable Energy Systems
>>> www.oregonsolarworks.com
>>> 541-218-0201
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change email address & settings:
>>>  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>>  www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>>  www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/04aad861/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 130249 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/04aad861/attachment-0001.png>


More information about the RE-Wrenches mailing list