[RE-wrenches] 600 v pv lead separation

william at millersolar.com william at millersolar.com
Wed Apr 9 15:54:00 EDT 2014


Brian:

 

You and I were right on-target with our evaluation.  Below is the message I
received from Morningstar:

 

The partition was added to satisfy UL/ETL requirements to prevent
co-mingling of high voltage(600V) input wires and low voltage battery and
communication wiring.   If the insulation on your battery and/or
communication cabling is rated for 600V, co-mingling shouldn't be an issue.
However, if the insulations is not rated for high voltage, we would suggest
leaving the divider intact.

 

I applaud Moringstar for backing down on their original instructions and
first email reply.  It is unfortunate that they were not more precise in
their original instructions-some installers may have wasted time and money
on conduit and partitions.  

 

I don't know if I could find wire not rated for 600 volts, so this is really
a non-issue.

 

William Miller

 

 

 

Lic 773985

millersolar.com

805-438-5600

 

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Brian
Mehalic
Sent: Monday, April 07, 2014 11:46 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 600 v pv lead separation

 

I don't know, but maybe it's a provision for using lower voltage rated wire
for the batteries?

 

Brian

 

> On Apr 7, 2014, at 2:17 PM, William Miller <
<mailto:william at millersolar.com> william at millersolar.com> wrote:

> 

> Colleagues:

> 

> I am installing a set of Tristar 600 volt input charge controllers. There
are separate compartments for PV and battery leads. Reviewing the 2014 NEC,
I see no requirement that these sets of leads be separated.

> 

> I wrote to the manufacturer just now asking the same question.

> 

> Have any of you looked into this yet?

> 

> Thanks in advance. 

> 

> William Miller

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140409/627fdc01/attachment-0001.htm>


More information about the RE-Wrenches mailing list