[RE-wrenches] NEC 2014 110.21(B)(1) ANSI question

Dan Fink danbob88 at gmail.com
Mon Mar 31 09:48:14 EDT 2014


Aha! It appears that NEC2014 did resolve the discrepancies with IFC 2012
that were in NEC 2011, no trumping with the AHJ needed.

I think I'm interpreting correctly that the only situations where NEC
requires white on red, reflective, is DC source circuits on or inside a
building (631.(G)(3), systems equipped with rapid shutdown, and
 stand-alone systems  690.56(C).  (The typo in that one is what threw me
for a loop, the marking reference is incorrect)

Everything else seems fall under 110.21(B).



Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342




On Mon, Mar 31, 2014 at 6:38 AM, Dan Fink <danbob88 at gmail.com> wrote:

> Esteemed Wrenches;
>
> I'm finding references online to 110.21(B)(1) requiring field applied
> hazard labels to comply with ANSI Z535.4-2011, but my NEC2014 book only
> refers to ANSI in an informational note for "guidelines" and I'm not seeing
> it in the errata.
> Does this mean ANSI-style labels (orange "warning" at top, black on white
> text below) are allowed but not required now? These also conflict with IFC 2012
> 605.11.1 in a few cases.
>
> Which trumps which, NEC2014 or IFC2012 as far as labels go?
>
> Thanks in advance.
>
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckville Publications LLC
> NABCEP / IREC accredited Continuing Education Providers
> 970.672.4342
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140331/bf1f0e40/attachment-0001.htm>


More information about the RE-Wrenches mailing list