[RE-wrenches] AC Combiner with main breaker as system disconnect
Mark Richardson
MRichardson at NewYorkLightEnergy.com
Thu Mar 13 12:08:20 EDT 2014
Hi All,
Just wondering if someone could confirm or expand on the assertion in Jason’s document that:
“NEC Article 690.64(A) allows a Line‐Side AC connection to busbars, conductors, or lugs at any
point between the customer’s side of the utility meter, and the service disconnect. Many folks
call this a “line‐side tap”, which leads to confusion with the “10‐foot tap rule” and Article
240.21(B). Tap rules and Article 240 do not apply here (emphasis added). These aren’t feeders, and service
entrance cables don’t have overcurrent protection”
Our engineers and design teams have always considered the Tap rules (Article 240, et al.) when utilizing a supply/line side connections and the utility here looks at this as a “separately derived service.”
Thanks,
Mark Richardson
US Light Energy
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Wednesday, March 12, 2014 8:13 PM
To: glenn.burt at glbcc.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
Glenn,
It may be that the equipment sold in your region is that way, but my experience is the opposite. I just looked in my electrical service panel at my home to check my sanity and it is 10,000A rated. So is every single-phase breaker sold at Home Depot or Lowes. You can’t put 10k breakers in a 25,000AIC panel unless you know the fault current is under 10kA.
I can’t argue with what you see, but you may be misinterpreting the ratings on the equipment. You may be reading something on the actual breaker, but that does not mean that it is 20kAIC in the panel. It has to be tested and listed with the panel. Again, the key is to confirm what the rating of the panel is. That is located on the inside cover or you can get that from the manufacturer.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Glenn Burt
Sent: Wednesday, March 12, 2014 4:51 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
Bill,
I have never seen a main breaker in a residential main load center (say 200A) that has a rating of less than 20k AIC. Is there somewhere else in the panel that changes this?
Glenn
From: re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Wednesday, March 12, 2014 7:24 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
Glenn,
The vast majority of service equipment for residences is rated 10k AIC. Although utilities may say they have some residential services that exceed 10k short circuit availability, it is still pretty rare.
Using single phase gear on a 3-phase commercial installation is a different story. Perhaps this is what you were referring to when talking about 10k AIC being too low.
I don’t people to get the idea that you have to check the fault current of every PV installation. You should only have to check fault current on a new service. Simply checking the ratings of the exist service equipment at an installation is sufficient to know what the minimum AIC rating of the equipment must be. The utility is not legally allowed to increase the fault current on a service above the service equipment ratings unless it is part of a service upgrade and the service equipment is being replaced.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Glenn Burt
Sent: Wednesday, March 12, 2014 3:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
Beware of breakers used as service disconnects. Most in the range suitable for a supply side connections for PV are really branch circuit rated with 10k AIC which is generally too low for the utility fault current they may be exposed to.
If you can get a statement from the utility with available fault current at the install site you might sneak one in. If you don't want to go to this trouble, use the rating of the exiting main breaker as a minimum value. Usually 20-25k AIC.
________________________________
From: Brian Teitelbaum<mailto:bteitelbaum at aeesolar.com>
Sent: 3/12/2014 17:32
To: RE-wrenches<mailto:re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
One big omission, in the otherwise fine Soligent white paper, is that the 60A minimum disconnect has to be rated as “Service Equipment”. Generally this means a “Heavy-Duty” safety switch or Service-rated load center with Main breaker.
I don’t see why an AC breaker panel, with a Main breaker, couldn’t act as the PV system disconnect, as long as it’s Service-rated, a minimum of 60A, and the utility does not require an external-handle disconnect, lockable in the off position. Many utility companies still do.
Brian Teitelbaum
AEE Solar
From: re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 12, 2014 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Combiner with main breaker as system disconnect
Don't utter the word tap. :)
See:
http://www.soligent.net/documents/HappyLandings_v3.pdf
We usually specify a fusible disconnect for overcurrent protection when grouping the PV AC combiner with the main premises disconnect is not practical.
Jason Szumlanski
Fafco Solar
On Wed, Mar 12, 2014 at 1:31 PM, <kevin at renovusenergy.com<mailto:kevin at renovusenergy.com>> wrote:
I am trying to determine whether an AC combiner panel (for multiple inverter outputs) with main breaker can be also used as the PV system disconnect?
This is for a line tap situation. I am accustomed to doing these systems with an AC combiner, and separate enclosure for a breaker style, line tap over current protection.
Any thoughts/comments would be appreciated.
Thanks,
Kevin
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
________________________________
[http://static.avast.com/emails/avast-mail-stamp.png]<http://www.avast.com/>
This email is free from viruses and malware because avast! Antivirus<http://www.avast.com/> protection is active.
________________________________
[http://static.avast.com/emails/avast-mail-stamp.png]<http://www.avast.com/>
This email is free from viruses and malware because avast! Antivirus<http://www.avast.com/> protection is active.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140313/0252ec4f/attachment-0001.htm>
More information about the RE-Wrenches
mailing list