I'm a Generac service tech and have some experience installing gaseous
generators (their term). I don't have any experience with freezing, being
in the Caribbean.
Virtually every installation not designed by a tech will have fuel piping
that is too small. The 20KW Generac Guardian needs a minimum 3/4" pipe but
we typically install 1" TRACPIPE to allow for more volume. I have seen
plumbers install two lengths of 4ft flexible pipe designed for stoves. A
domestic stove requires about 50K btu/hr, a 20KW LPG generator requires
about 400,000 btu/hr.
We normally use twin stage regulators but if the run is long we may use two
separate stages. As the intermediary stage is higher pressure it can use a
smaller pipe size.
As I understand it, the larger pipe before the generator allows the gas to
smooth out any standing waves or pulses.
On Mon, Feb 17, 2014 at 8:04 PM, Ray Walters <ray at solarray.com> wrote:
> Wow, so would you need a small expansion tank to dampen that out? IS
> that even allowed on LPG? What was the cure?
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer303 505-8760
>
> On 2/17/2014 4:19 PM, toddcory at finestplanet.com wrote:
>
> to further complicate things, i have seen "regulator oscillation" problems
> with 2 in series.
>
>
>
> todd
>
>
>
>
>
>
>
>
>
> On Monday, February 17, 2014 2:30pm, "Ray Walters" <ray at solarray.com><ray at solarray.com>said:
>
> Alot of these generator setups need 2 regulators, so usually the regular
> one stays at the tank, size the pipe for the flow rate ( just like wire and
> amps.... ;-) .) and put the 2nd regulator right at the generator.
>
> R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed
> Master Electrician Solar Design Engineer 303 505-8760 On 2/17/2014 3:17
> PM, Larry Crutcher, Starlight Solar Power Systems wrote:
>
> Ditto Tom, seen this too often in Mexico. I carry a manometer to make
> check the pressure at the LP input to the generator with the engine
> running. Make sure it is at/above 11" WC when it starts to act up. If the
> regulator is at the tank, long vapor runs can cause too much pressure loss.
> Larry
>
>
> On Feb 17, 2014, at 1:36 PM, Tom Duffy <Tom at thesolar.biz> wrote:
>
> Hi Guys
> We have had "icing" problems here in Central America as well where the
> gas company put in 1/2' pipe to a 12K Gillette Generator, same description
> the gen would initially start and run fine but then it went erratic the
> Radian didn't like it, the customer wanted to blame the Radian (I was sure
> it wasn't)
> The installer/dealer couldn't figure it out. I went out and immediately
> saw the small pipe, plus they had bent a crimp into the incoming fuel line
> as well. 3/4 " line fixed the whole thing. LP has a lot of moisture and will
> always have delivery problems with funky installation of pipe. Seems that a
> lot of gas guys just hook up kitchen ranges (Here)
> Kind regards
> *Tom Duffy*
> *Senior Solar Design Engineer*
> <image002.png>
> *E-Mail: **tom at thesolar.biz <tom at thesolar.biz>*
> *Panama Office: **507-6126-1253*
> *Direct Toll Free:* *888-503-6772 <888-503-6772>*
> *International: **575-539-2111 <575-539-2111>*
> *SKYPE Address: **thesolarbiz*
> *Although no trees were killed in the sending of this message, a large
> number of electrons were terribly inconvenienced.*
> *Confidentiality Notice*: This message including any attachments is for
> the sole use of the intended recipient and may contain confidential and
> privileged information. Any unauthorized review, use, disclosure or
> distribution is prohibited. If you are not the intended recipient, please
> contact the sender and delete any copies of this message.
>
>
> _______________________________________________ List sponsored by Home
> Power magazine List Address: RE-wrenches at lists.re-wrenches.org Change
> email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List
> rules & etiquette: www.re-wrenches.org/etiquette.htm Check out
> participant bios: www.members.re-wrenches.org
>
>
>
>
> Sent from Finest Planet WebMail.
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
--
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140217/f02bf42d/attachment-0001.htm>
More information about the RE-Wrenches
mailing list