Allan:

 

Thanks for that interpretation.  I know some German high school students.  I
may see if they can interpret the original for me.  Seems pretty cryptic.

 

William

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Tuesday, February 11, 2014 8:17 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] From the Sunny Island manual

 

William,
Before I read your interpretation, mine was quite different, and I think
simpler. I read it as saying simply that if the Sunny Island sees AC, it can
take current from that source if it needs it for charging. A fuse, if blown,
is no different than having no external AC source from which to charge. 
Nothing else meant by this sectin.
Allan

Allan Sindelar
 <mailto:Allan at positiveenergysolar.com> Allan at positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.

A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com <http://www.positiveenergysolar.com/> 

On 2/11/2014 9:04 PM, william at millersolar.com wrote:

Friends:

 

Below is a quote from the Sunny Island manual.  I am interested if anyone
can interpret this for me, please.

 

If there are no additional fuses installed between the generator or utility
grid and the Sunny Island, the Sunny Island knows whether it has a
connection to the utility grid/to the generator. The Sunny Island can then
draw current from the utility grid/from the generator.

 

If there are additional fuses or switches installed between the Sunny Island
and the utility grid/ the generator, the Sunny Island cannot determine
whether fuses or switches are separated or whether there is no voltage
available from the utility grid/the generator. In either case the Sunny
Island cannot charge its battery and the loads that are in operation will
discharge the Sunny Island battery. Check the additional fuses and switches
regularly in order that the Sunny Island battery only discharges when there
is no voltage available from the utility grid/the generator.

 

Here is what I think it means:  if there is additional power distribution
connected to the Sunny Island AC input, those loads may be powered by
inversion, inadvertently depleting the batteries.  What is unusual here is
that with a standard off-grind inverter, loads connected to the input side
can never be powered by the batteries, but they can be with an AC coupled
inverter?  Is this correct?

 

Also, I have not found it in the manual although I have looked:  Can the
Sunny Island provide generator support (sync to and provide additional power
to loads that exceed the capability of the generator?

 

Thank you all very much.

 

William Miller

 






_______________________________________________
List sponsored by Home Power magazine
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140211/1d381611/attachment-0001.htm>


More information about the RE-Wrenches mailing list