Jay:

 

It is meant for installation immediately adjacent to the inverters.  I
believe we need to be installing OCP adjacent to the batteries.

 

Wm

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Tuesday, February 11, 2014 6:56 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island battery OCP

 

HI William,

 

I agree with your choices below, but I"m  curious why you decided against
the midnite Epanel for the SI?

 

thanks

 

jay

 

peltz power

 

 

On Feb 10, 2014, at 9:33 PM, <william at millersolar.com> wrote:





Friends:

 

Thanks for all of the replies.  Here is what I have learned so far

 

1.       The SMA fuse blocks are not UL listed for installation in the
USofA.

2.       The Square D switches are not high enough in amperage for battery
circuits.

3.       The bolt-switch idea is great if you want fuses and a pullout.  Not
for me.

4.       Our solution will be an Outback FX 1000 with three 250 amp
breakers.

 