i would love to see a spectrum analyzer's view of the fx's harmonics. does anyone have this available?
interesting (and sad) how silent outback is on this list now.
todd
On Monday, February 10, 2014 9:37pm, "Exeltech" <exeltech at yahoo.com> said:
> Bruce,
>
> The capacitors may or may not help, and could make things worse. If you've
> already encountered and solved this exact issue on other identical systems ..
> carry on.
>
> If not ...
>
> Switching power supplies have a double-whammy of being non-linear AND reactive.
> The reactive component is almost always a capacitive "front end" in the power
> supply. If the predominant issue happens to be harmonics .. then power-factor
> correction capacitors MAY help by filtering out some of the higher frequency
> aspects. If the predominant issue is the reactive front end of the power supply
> .. caps could make the situation worse.
>
> As a side-note, PF correction caps connected across the output of an inverter can
> cause the inverter's voltage control loop to go unstable, and blow the inverter.
> Not a guaranteed failure .. but an enhanced possibility.
>
>
> Dan