[RE-wrenches] -48 Volts at the Phone Company

Exeltech exeltech at yahoo.com
Mon Feb 3 15:17:32 EST 2014


Keith,

Another wrench commented about the Exeltech inverters being capable of working with a -48V battery system.

His info was good.  The DC input is "floating" on XP and MX inverters, and may be used in positive-ground telecom battery systems as well as negative ground systems .. such as off-grid, etc..

The MX 120V models are available up to 20 kW, 40 kW in 240V, and 60 kw in 208V three phase.  The 120V models can grow incrementally in 1 kW steps; 240V in 2 kW steps; and the three-phase grows in 3 kW steps.

You'll have to contact their sales department for more info.

By the way .. my own jaded view of "kVA" ratings .. they're marketing hype to make an inverter look more capable on paper than it really is.


Dan

--------------------------------------------
On Thu, 1/30/14, Keith Cronin <electrichi01 at yahoo.com> wrote:

Subject: [RE-wrenches] -48 Volts at the Phone Company
To: "RE-Wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Thursday, January 30, 2014, 10:16 PM
 
 Hi folks

Any inverters in the marketplace that will happily take -48 volts off the phone companies standard battery banks they use to backup their phone network for us?
 
Client wants to drive a 15kva load and replace and existing conventional UPS system that was rated for 40kva.

Thanks

Keith Cronin



More information about the RE-Wrenches mailing list