[RE-wrenches] (RE-wrenches) 2x200 amp meter main panel question

Bill Brooks billbrooks7 at yahoo.com
Thu Jan 23 17:31:46 EST 2014


William and John,

 

A "320" as it is affectionately called is a 400-amp panel with a 320-amp
continuous duty. This is identical to two 200-amp panels that each has a
160-amp continuous duty-that we put 40-amp breakers into on a routine basis.
The "busbars" are rated for 200-amps each, just like a 200-amp panel. But
just as you cannot run a 200-amp panel at 200-amps continuously (only
160-amps continuously), you cannot run a 400-amp panel at more than 320-amps
continuously-it is the exact same thing.

 

Bill.

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of John Powell
Sent: Thursday, January 23, 2014 1:32 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] (RE-wrenches) 2x200 amp meter main panel question

 

Thanks WIlliam,

 

Some of the old Milbank units are 320 amp rated socket.  The Murray 2 x
200's are 400 amp rated.

 

Best regards,

 

Abe

-- 

J. Abraham Powell

President

Solforce Systems, Inc.

224-G South Milpas Street

Santa Barbara, CA 93103

Phone: (805) 695-0015

Fax: (805) 565-1661

Cell:  (805) 895-2355

e-mail:  abe at solforce.com <mailto:abe at solforce.com> 

 





 

On Jan 23, 2014, at 12:30 PM, William wrote:





John: 

These panels are typically rated only 320A continuous duty, so I think your
numbers would not compute.

William




On Jan 23, 2014, at 11:31 AM, John Powell <abe at solforce.com
<mailto:abe at solforce.com> > wrote:

 

Has anyone tried to connect one 40 amp inverter output circuit to each of
the two breakers on a 2 x 200AMP single meter main panel in California?  

 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org
<mailto:RE-wrenches at lists.re-wrenches.org> 

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>


Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

 



---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140123/1544e99f/attachment-0001.htm>


More information about the RE-Wrenches mailing list