[RE-wrenches] 2014 NEC
Bill Brooks
billbrooks7 at yahoo.com
Tue May 27 15:17:53 EDT 2014
Nick and Jay,
There is a basic problem that products are not currently available to specifically address this application. I know Enphase has done a lot of research lately about this issue, so they may have uncovered problems that were previously not known. My information is that the products are actually bi-directional devices. GFCIs are not bi-direction and can fail with voltage on the load side of the device. It is possible that some AFCIs have the same problem.
This AFCI provision is a requirement that was sold to UL and the Code Making Panel with the assurance from a very large breaker manufacturer that developing products for this application was simple and straightforward.
That manufacturer has not stepped forward with a product and so we find ourselves in 90.4 land (use the previous version of the code). Some AHJs have chosen not to read it that way and have been requiring micro-inverter systems to be installed raceways (even though not compatible with raceways). NFPA likely have to issue an official interpretation on this since it is unclear whether a product will be developed in the reasonable future.
Bill.
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Tuesday, May 27, 2014 11:32 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 2014 NEC
Hi nick
Good to know, I was told this by bill brooks at a training a few months ago.
Jay
Sent from my iPhone
On May 27, 2014, at 9:00 AM, Nick Soleil <nsoleil at enphaseenergy.com <mailto:nsoleil at enphaseenergy.com> > wrote:
Hi Jay,
It is not acceptable to wire the AFCI breaker with the utility power on the output of the AFCI breaker. That does not meet the specifications for the AFCI breakers. These breakers are sensitive to having voltage on their output when the breaker is opened, which can damage the AFCI breakers.
Currently, there are no AFCI circuit breakers that are listed for back-feed.
On Tue, May 20, 2014 at 8:10 AM, jay peltz <jay at asis.com <mailto:jay at asis.com> > wrote:
HI Will,
You can do this.
Take a standard breaker panel, install a Arc fault and run the wiring from the enphase like it is the grid: ie into the main lugs.
Then this will go out through the breaker in the correct fashion, and onto the main panel.
jay
peltz power
PS as to the code, they want it this way
On May 20, 2014, at 7:59 AM, Will White wrote:
Wrenches,
Is anyone else having problems with inspectors and the 2014 NEC? In Mass we’re having all kinds of issues with inspectors requiring/allowing an array of different things for 690.12 rapid shut down ranging from roof top disconnects, disconnects on the side of a house 20’ up, disconnects in attics, or only disconnects that can be activated on the ground. It varies between inspectors.
We’re also having problems with one inspector requiring arc fault breakers on Enphase even though there are no UL listed arc fault breakers that can be back fed or he wants us to run the trunk cable in a raceway.
It’s getting very difficult to install in Mass.
Thanks,
Will
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 <tel:802.223.7804> | mobile 802.234.3167 <tel:802.234.3167> | fax 802.223.8980 <tel:802.223.8980>
<http://www.rgsenergy.com/> RGSEnergy.com | <mailto:william.white at rgsenergy.com> william.white at rgsenergy.com
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
Cordially,
Nick Soleil
Field Applications Engineer
Enphase Energy
Mobile: (707) 321-2937
<http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten>
<http://enphase.com/enlighten_content/myenlighten-launch-site/?utm_source=MyEnlightenPromo&utm_medium=Email_Sig&utm_campaign=MyEnlighten> MyEnlighten is Coming. Get Ready
<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>
1420 North McDowell
Petaluma, CA 94954
www.enphase.com <http://www.enphaseenergy.com/>
P: (707) 763-4784 x7267
F: (707) 763-0784
E: nsoleil at enphaseenergy.com <mailto:nsoleil at enphaseenergy.com>
NABCEP Certified Solar PV Installer #03262011-300
California C10 Licensed Electrician #986315
Texas Master Electrician #284451
“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion to fission. And it just so happens that there’s an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it’s wireless!”
- William McDonough
This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140527/0d8664f3/attachment.htm>
More information about the RE-Wrenches
mailing list