[RE-wrenches] 2014 NEC
Will White
William.White at rgsenergy.com
Tue May 20 10:59:46 EDT 2014
Wrenches,
Is anyone else having problems with inspectors and the 2014 NEC? In Mass we're having all kinds of issues with inspectors requiring/allowing an array of different things for 690.12 rapid shut down ranging from roof top disconnects, disconnects on the side of a house 20' up, disconnects in attics, or only disconnects that can be activated on the ground. It varies between inspectors.
We're also having problems with one inspector requiring arc fault breakers on Enphase even though there are no UL listed arc fault breakers that can be back fed or he wants us to run the trunk cable in a raceway.
It's getting very difficult to install in Mass.
Thanks,
Will
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com<http://www.rgsenergy.com/> | william.white at rgsenergy.com<mailto:william.white at rgsenergy.com>