[RE-wrenches] Battery cable crimper

Ray Walters ray at solarray.com
Fri May 2 01:43:25 EDT 2014


Hi Glenn;

Quick Cable that provides the UL listed cables and lugs, also sells this 
tool for those lugs. I don't know about UL testing, etc.   Is the 
inspector actually asking to see the tool?   The Greenlee tool that 
makes the same type crimp is definitely good stuff.  However, there is 
no substitute for good craftsmanship. A lot of equipment with UL 
listings is junk, so UL by itself is no guarantee of quality or 
safety.    I think we can all dig around our household for more examples 
of inferior products sporting the UL emblem.  (Consider those 39 cent AC 
receptacles that break plastic off around the ground opening, the first 
time you plug something into them, or later, allow plugs to fall half 
out of the receptacle, because they've lost their "spring".)
Like any tool, the hammer crimper can be misused. The biggest problem 
I've seen is folks not stripping enough insulation off the cable, and so 
not enough copper goes past the crimp into the lug. These failed the 
"pull" test.  We once had to redo a whole battery bank of crimps because 
the previous installer had not stripped enough insulation off. See below:

THHN Stiff Class B wire, and Corrosion don't help either.  Believe it or 
not, that lug cleaned up nicely once soaked in baking soda water for 1/2 hr.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 5/1/2014 5:42 PM, Glenn Burt wrote:
>
> But does it make a listed crimp?
>
> Are any lug manufacturers accepting it as a tool that will meet their 
> requirements for a certifiable crimp?
>
> I did a lot of research on cables, stranding and manufacturers methods 
> and tools used to make crimps a few years ago (posted to list in '09 & 
> 10). The ones I looked at only certified their products (lugs) when 
> used with specified tools.
>
> *From:*re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Solar
> *Sent:* Thursday, May 01, 2014 9:12 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Battery cable crimper
>
> From what I'm hearing I think may go with a hammer crimper. Being able 
> to crimp in a box might be handy, but it sounds like the quality of 
> the crimps produced by the  hammer crimper is where it's at.
>
> Maybe a hammer and a long handle?!
>
> Thanks!
>
> Jesse
>
> RE-Power
>
> Sent from my iPhone
>
>
> On May 1, 2014, at 1:08 AM, Ray Walters <ray at solarray.com 
> <mailto:ray at solarray.com>> wrote:
>
>     Here's all the battery lug crimpers I tried over the years in
>     order of the best to worst connections they produced:
>     <bdbagfhj.jpg>
>     Yes, believe it or not: the venerable Hammer crimper makes
>     excellent connections.  Its also Cheap, but its Slow, cumbersome,
>     and can't be used in a J box.
>     The V and indent connection with the thin wall lugs makes the
>     ideal battery and DC connections.  They look just like the crimps
>     from Outback, Trace, Midnite,etc. I've cut them open on a band
>     saw, and the fine strands are practically fused together into an
>     almost solid cross section of copper with no voids, but no tearing
>     of strands at the edges either.
>     This crimper goes out on most jobs, as it fits in the bottom of
>     the tool box.
>     <fhibhicd.jpg>
>     The Greenlee indentor crimper makes the same V  crimp connection
>     as the hammer crimper, but is faster, and can be used up in a j
>     box.  More expensive, and adjuster readings can't be counted on. 
>     I tighten the adjuster until I can just pull the handle down with
>     putting some body weight into it, but not so much that I'm
>     standing on it or straining the tool.  Depending on the cable and
>     lug combination, the setting may be 2 sizes smaller with thin wall
>     lugs.
>     Overall, this is what we use most of the time.  I found that this
>     set in a drill vice makes a good bench crimper, when you need to
>     do a batch of battery jumpers.
>
>     <fcafcjdi.jpg>
>     I used this one for many years, also a V crimper, but has
>     different dies.  Crimp quality was not as good, as the dies tore
>     into the lug some.  Also changing the dies took time, and we once
>     lost one of the dies, and it took months to get a replacement. 
>     Not adjustable for different lug and cable combos.
>
>     <bfdddceg.jpg>
>     The "UL" Hex type crimper that you will find at regular electrical
>     supply houses.  Quite expensive, but I am not a fan.  The dies
>     bend slightly under pressure and so the hex crimps are not aligned
>     with each other.  The dies tear the lugs, leaving sharp edges that
>     can tear heat shrink, and there is no adjustment available to
>     account for different cable and lug combinations.
>     We have  X flex from Cobra, MTW from Quick Cable, and some DLO
>     from another supplier.  All are UL listed 4/0 and all somewhat
>     different in diam. and how the strands crush.  I have had a
>     connection failure with this tool, and cutting through a cross
>     section of the lug was not as solid a crimp as the V type.  I
>     removed this tool from our shop, to avoid mistakes.
>     I'm sure with regular Class B stranded THHN, and the heavy wall,
>     color coded lugs, that this is a good tool, but for battery
>     connections, it does not work as well with thin wall lugs.
>     Finally, I do not recommend the heavy wall, long barrel lugs on
>     batteries.  The square lug end is just too big and thick, and
>     can't bolt to battery terminals in some cases.  We have had to
>     grind away a corner for instance to have the heavy wall lugs land
>     on an battery Flag terminal.
>     The heavy terminals some what negate the advantages of flex cable
>     in the first place.
>
>     R.Ray Walters
>
>     CTO, Solarray, Inc
>
>     Nabcep Certified PV Installer,
>
>     Licensed Master Electrician
>
>     Solar Design Engineer
>
>     303 505-8760
>
>     On 4/30/2014 7:33 PM, Solar wrote:
>
>         I'd love a battery crimper, but a little out of my price range.
>
>         I think a hand crimper will do.
>
>         Jesse
>
>         Sent from my iPhone
>
>
>         On Apr 30, 2014, at 1:42 PM, Jerry Shafer
>         <jerrysgarage01 at gmail.com <mailto:jerrysgarage01 at gmail.com>>
>         wrote:
>
>             hydraulic or long handle bog difference in price
>
>             On Apr 30, 2014 8:32 AM, "Solar" <dahlsolar at gmail.com
>             <mailto:dahlsolar at gmail.com>> wrote:
>
>             Hello all,
>
>             I am looking for recommendations for a battery cable
>             crimper.  I'd love to get one with the dies built in, but
>             the ones I've looked at are only for non-fine strand wire.
>
>             Suggestions?
>
>             Thanks!
>
>             Jesse
>
>
>
>
>
>
>             Sent from my iPhone
>             _______________________________________________
>             List sponsored by Home Power magazine
>
>             List Address: RE-wrenches at lists.re-wrenches.org
>             <mailto:RE-wrenches at lists.re-wrenches.org>
>
>             Change email address & settings:
>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>             List-Archive:
>             http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>             List rules & etiquette:
>             www.re-wrenches.org/etiquette.htm
>             <http://www.re-wrenches.org/etiquette.htm>
>
>             Check out participant bios:
>             www.members.re-wrenches.org
>             <http://www.members.re-wrenches.org>
>
>             _______________________________________________
>             List sponsored by Home Power magazine
>
>             List Address: RE-wrenches at lists.re-wrenches.org
>             <mailto:RE-wrenches at lists.re-wrenches.org>
>
>             Change email address & settings:
>             http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>             List-Archive:
>             http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>             List rules & etiquette:
>             www.re-wrenches.org/etiquette.htm
>             <http://www.re-wrenches.org/etiquette.htm>
>
>             Check out participant bios:
>             www.members.re-wrenches.org
>             <http://www.members.re-wrenches.org>
>
>
>
>
>         _______________________________________________
>
>         List sponsored by Home Power magazine
>
>           
>
>         List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>
>           
>
>         Change email address & settings:
>
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>           
>
>         List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>           
>
>         List rules & etiquette:
>
>         www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>
>           
>
>         Check out participant bios:
>
>         www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>
>           
>
>     _______________________________________________
>     List sponsored by Home Power magazine
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140501/cdca7d44/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ggaeaibb.jpg
Type: image/jpeg
Size: 50576 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140501/cdca7d44/attachment.jpg>


More information about the RE-Wrenches mailing list