[RE-wrenches] Article 690, or The Haves Vs. Have Nots
Drake
drake.chamberlin at redwoodalliance.org
Wed Apr 30 09:56:58 EDT 2014
There are good reasons to want to put AC
combiners under modules, but some reasons not to
want to. An AC breaker is far more likely to trip
than a DC string fuse, due to the surge
availability. As a PV system is designed to last
a minimum of 25 years, the installer might not be
the one to sort out problems decades down the line.
A strategy I prefer would be to use a SolaDeck as
a junction box. Run small wires to a convenient AC combiner location.
At 12:43 PM 4/29/2014, you wrote:
>Dave
>
>I agree, in the case of microinverters, you
>already have a main PV System disconnect at the
>Load Panel to shut down the system that is
>readily accesible. I would consider the
>disconnect on the roof as a supplemental
>disconnect for the purposes of maintenance by
>authorized personal that only needs to be accessible.
>
>Bill
>
>
>On Tue, Apr 29, 2014 at 8:44 AM, Dave Click
><<mailto:daveclick at fsec.ucf.edu>daveclick at fsec.ucf.edu> wrote:
>I think 240.24(A)(4) allows the installation of
>the inverter OCPDs in the SolaDeck hidden under a module.
>
>240.24 Location in or on Premises.
>(A) Accessibility. Overcurrent devices shall be
>readily accessible and shall be installed so
>that the center of the grip of the operating
>handle of the switch or circuit breaker, when in
>its highest position, is not more than 2.0 m (6
>ft 7 in.) above the floor or working platform,
>unless one of the following applies:
>...
>(4) For overcurrent devices adjacent to
>utilization equipment that they supply, access
>shall be permitted to be by portable means.
>
>
>And if panelboards / fused safety switches are
>allowed to have screwed-down covers over the
>OCPDs, I'd think that installing a removable
>module over these OCPDs would meet NEC. I guess
>an AHJ could argue that this requires TWO covers
>be removed, unlike a panelboard or a switch.
>
>DKC
>
>
>On 2014/4/29, 11:15, Jason Szumlanski wrote:
>>690.9(D) is not applicable to the original
>>discussion because we were talking about an
>>Inverter output circuit, not a PV Source or Output circuit.
>>
>>690.34 may apply if you call a SolaDeck with
>>breakers a junction box, but I can see that
>>being a stretch in the mind of many.
>>
>>My and Ray's question about the screws on the
>>SolaDeck cover itself requiring a tool to
>>render it accessible is still an issue if the
>>breakers themselves need to be "readily
>>accessible," but that would also apply to a
>>Midnite MNPV, which also has a cover with a screw.
>>
>>
>>Jason Szumlanski
>>
>>On 4/28/2014 5:57 PM, Bill Brooks wrote:
>>>
>>>Read 690.9(D) and 690.34. Not sure where this
>>>hysteriarun for the border sentiment is coming from.
>>>
>>>
>>>
>>>690.9(D) Photovoltaic Source and Output Circuits. Listed PV
>>>
>>>overcurrent devices shall be required to provide overcurrent
>>>
>>>protection in PV source and output circuits. The overcurrent
>>>
>>>devices shall be accessible but shall not be required to
>>>
>>>be readily accessible.
>>>
>>>
>>>
>>>690.34 Access to Boxes. Junction, pull, and outlet boxes
>>>
>>>located behind modules or panels shall be so installed that
>>>
>>>the wiring contained in them can be rendered accessible
>>>
>>>directly or by displacement of a module(s) or panel(s) secured
>>>
>>>by removable fasteners and connected by a flexible
>>>
>>>wiring system.
>>>
>>>
>>>
>>>This is not a change. Please help me understand the concern.
>>>
>>>
>>>
>>>Bill Brooks.
>>>
>>>
>>>
>>>
>>>
>>>From:
>>><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org
>>>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray Walters
>>>Sent: Monday, April 28, 2014 2:23 PM
>>>To: RE-wrenches
>>>Subject: Re: [RE-wrenches] (no subject)
>>>
>>>
>>>
>>>Interesting so does "require a tool" include
>>>taking a screw off the cover plate of the combiner box, too?
>>>What a game changer. I'm going to Mexico for
>>>my next project; I'll actually enjoy even more
>>>being the sole AHJ on the project.
>>>
>>>
>>>R.Ray Walters
>>>CTO, Solarray, Inc
>>>Nabcep Certified PV Installer,
>>>Licensed Master Electrician
>>>Solar Design Engineer
>>><tel:303%20505-8760>303 505-8760
>>>On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>>>
>>>Readily accessible is now defined in the 2014
>>>NEC. Installing OCPDs underneath a module is
>>>a major faux paux, and I cant imagine any AHJ
>>>thinking otherwise. Having to remove a module
>>>in order to reset a breaker, what a drag.
>>>
>>>
>>>
>>>"Capable of being reached quickly for
>>>operation, renewal or inspection without
>>>requiring those concerned to use a tool, to
>>>climb over, remove obstacle or other.
>>>
>>>
>>>
>>>Michael
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>On Apr 28, 2014, at 10:29 AM, William Miller
>>><<mailto:william at millersolar.com>william at millersolar.com> wrote:
>>>
>>>
>>>
>>>You call it a solar panel, I call it a glass j-box cover plate.
>>>
>>>William
>>>
>>>Miller Solar
>>>
>>>
>>>On Apr 28, 2014, at 9:21 AM, Jason Szumlanski
>>><<mailto:jason at fafcosolar.com>jason at fafcosolar.com> wrote:
>>>
>>>If that is the interpretation,
>>>I don't see how the breakers are "readily accessible" in a SolaDeck
>>>mounted anywhere, regardless of whether it is under a module. It
>>>requires removal of four screws (using a tool) to access the breakers
>>>inside the enclosure. It's all up to the AHJ. It has not been an issue
>>>locally here. I can see how other jurisdictions may not
>>>concur.
>>
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches..org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>>_______________________________________________
>>
>>List sponsored by Home Power magazine
>>
>>
>>List Address:
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>
>>Change email address & settings:
>>
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>
>>List-Archive:
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>
>>List rules & etiquette:
>>
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>
>>Check out participant bios:
>>
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address:
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>
>
>--
>William Hoffer
>161 SE Fourth Ave
>P.O. Box 1823
>White Salmon, WA 98672-1823
><mailto:bhoffer at sunergyengineeringservices.com>sunengser at gmail.com
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140430/0f2ebf9c/attachment.htm>
More information about the RE-Wrenches
mailing list