[RE-wrenches] Article 690, or The Haves Vs. Have Nots
Jason Szumlanski
jason at fafcosolar.com
Wed Apr 30 09:56:56 EDT 2014
Yeah, #10 wire is pretty cheap, especially when purchased in bulk, as are
readily available 100A Square D NEMA 3R load centers and breakers. There
isn't a great cost savings in terms of material. Sometimes it's just easier
to make a single home run. Every job is different. We do it both ways.
Sometimes there isn't enough space near the meter or existing distribution
for both a combiner and fusible disconnect or there are obstructions that
make it impractical. There are aesthetic concerns (usually overblown by the
homeowner or HOA).
What we really need is for Square D to start making main distribution
equipment with dedicated supply side lugs with OCPD built in. One can
dream...
Jason
On Wed, Apr 30, 2014 at 9:44 AM, jay peltz <jay at asis.com> wrote:
> Hi Jason,
>
> Always good to get a different view on how to do it.
> I've always found it easier and cheaper to pull the circuits off the roof
> to the AC combiner, so my overcurrent is in a different location
>
> Jay
> Peltz power
>
>
>
>
>
>
> On Apr 30, 2014, at 5:08 AM, Jason Szumlanski <jason at fafcosolar.com>
> wrote:
>
> Each microinverter string needs dedicated overcurrent protection. If
> combining strings on the roof for a single run back to the interconnection
> point, you need each string to have it's own breaker/fuse. The other option
> is to run each string back to the interconnection point separately, but for
> a 10kW system you have to do a supply side connection anyway on as typical
> 200A service, so combining strings somewhere is necessary, and a single run
> from the roof makes sense in many cases.
>
>
> Jason Szumlanski
>
> Fafco Solar
>
>
>
>
>
> On Tue, Apr 29, 2014 at 6:40 PM, jay peltz <jay at asis.com> wrote:
>
>> Follow up to Bill's point.
>>
>> For Micros I've installed a disconnect on the roof, but never a breaker
>> or fuse
>> Why install a breaker?
>>
>> jay
>>
>> peltz power
>>
>> On Apr 29, 2014, at 9:43 AM, Bill Hoffer wrote:
>>
>> Dave
>>
>> I agree, in the case of microinverters, you already have a main PV System
>> disconnect at the Load Panel to shut down the system that is readily
>> accesible. I would consider the disconnect on the roof as a supplemental
>> disconnect for the purposes of maintenance by authorized personal that only
>> needs to be accessible.
>>
>> Bill
>>
>>
>> On Tue, Apr 29, 2014 at 8:44 AM, Dave Click <daveclick at fsec.ucf.edu>wrote:
>>
>>> I think 240.24(A)(4) allows the installation of the inverter OCPDs in
>>> the SolaDeck hidden under a module.
>>>
>>> *240.24 Location in or on Premises.*
>>> *(A) Accessibility.* Overcurrent devices shall be readily accessible
>>> and shall be installed so that the center of the grip of the operating
>>> handle of the switch or circuit breaker, when in its highest position, is
>>> not more than 2.0 m (6 ft 7 in.) above the floor or working platform,
>>> unless one of the following applies:
>>> ...
>>> (4) For overcurrent devices adjacent to utilization equipment that they
>>> supply, access shall be permitted to be by portable means.
>>>
>>>
>>> And if panelboards / fused safety switches are allowed to have
>>> screwed-down covers over the OCPDs, I'd think that installing a removable
>>> module over these OCPDs would meet NEC. I guess an AHJ could argue that
>>> this requires TWO covers be removed, unlike a panelboard or a switch.
>>>
>>> DKC
>>>
>>>
>>> On 2014/4/29, 11:15, Jason Szumlanski wrote:
>>>
>>> 690.9(D) is not applicable to the original discussion because we were
>>> talking about an Inverter output circuit, not a PV Source or Output circuit.
>>>
>>> 690.34 may apply if you call a SolaDeck with breakers a junction box,
>>> but I can see that being a stretch in the mind of many.
>>>
>>> My and Ray's question about the screws on the SolaDeck cover itself
>>> requiring a tool to render it accessible is still an issue if the breakers
>>> themselves need to be "readily accessible," but that would also apply to a
>>> Midnite MNPV, which also has a cover with a screw.
>>>
>>>
>>> Jason Szumlanski
>>>
>>>>
>>>> On 4/28/2014 5:57 PM, Bill Brooks wrote:
>>>>
>>>> Read 690.9(D) and 690.34. Not sure where this “hysteria—run for the
>>>> border” sentiment is coming from.
>>>>
>>>>
>>>> *690.9(D) Photovoltaic Source and Output Circuits. *Listed PV
>>>>
>>>> overcurrent devices shall be required to provide overcurrent
>>>>
>>>> protection in PV source and output circuits. The overcurrent
>>>>
>>>> devices shall be accessible but shall not be required to
>>>>
>>>> be readily accessible.
>>>>
>>>>
>>>> *690.34 Access to Boxes. *Junction, pull, and outlet boxes
>>>>
>>>> located behind modules or panels shall be so installed that
>>>>
>>>> the wiring contained in them can be rendered accessible
>>>>
>>>> directly or by displacement of a module(s) or panel(s) secured
>>>>
>>>> by removable fasteners and connected by a flexible
>>>>
>>>> wiring system.
>>>>
>>>>
>>>> This is not a change. Please help me understand the concern.
>>>>
>>>>
>>>> Bill Brooks.
>>>>
>>>>
>>>>
>>>> *From:* re-wrenches-bounces at lists.re-wrenches.org [
>>>> mailto:re-wrenches-bounces at lists.re-wrenches.org<re-wrenches-bounces at lists.re-wrenches.org>]
>>>> *On Behalf Of *Ray Walters
>>>> *Sent:* Monday, April 28, 2014 2:23 PM
>>>> *To:* RE-wrenches
>>>> *Subject:* Re: [RE-wrenches] (no subject)
>>>>
>>>>
>>>> Interesting so does "require a tool" include taking a screw off the
>>>> cover plate of the combiner box, too?
>>>> What a game changer. I'm going to Mexico for my next project; I'll
>>>> actually enjoy even more being the sole AHJ on the project.
>>>>
>>>> R.Ray Walters
>>>>
>>>> CTO, Solarray, Inc
>>>>
>>>> Nabcep Certified PV Installer,
>>>>
>>>> Licensed Master Electrician
>>>>
>>>> Solar Design Engineer
>>>>
>>>> 303 505-8760
>>>>
>>>> On 4/28/2014 2:52 PM, Michael Morningstar wrote:
>>>>
>>>> Readily accessible is now defined in the 2014 NEC. Installing OCPD’s
>>>> underneath a module is a major faux paux, and I can’t imagine any AHJ
>>>> thinking otherwise. Having to remove a module in order to reset a breaker,
>>>> what a drag.
>>>>
>>>>
>>>> "Capable of being reached quickly for operation, renewal or inspection
>>>> without requiring those concerned to use a tool, to climb over, remove
>>>> obstacle or other.”
>>>>
>>>>
>>>> Michael
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> On Apr 28, 2014, at 10:29 AM, William Miller <william at millersolar.com>
>>>> wrote:
>>>>
>>>>
>>>>
>>>> You call it a solar panel, I call it a glass j-box cover plate.
>>>>
>>>> William
>>>>
>>>> Miller Solar
>>>>
>>>>
>>>> On Apr 28, 2014, at 9:21 AM, Jason Szumlanski <jason at fafcosolar.com>
>>>> wrote:
>>>>
>>>> If that is the interpretation,
>>>> I don't see how the breakers are "readily accessible" in a SolaDeck
>>>> mounted anywhere, regardless of whether it is under a module. It
>>>> requires removal of four screws (using a tool) to access the breakers
>>>> inside the enclosure. It's all up to the AHJ. It has not been an issue
>>>> locally here. I can see how other jurisdictions may not
>>>> concur.
>>>>
>>>>
>