[RE-wrenches] Stainless NEMA4x load center, SolarDeck w/ breakers
Kirpal Khalsa
solarworks at gmail.com
Wed Apr 23 16:48:08 EDT 2014
Friends,
I just discovered that Midnite Solar also has a 3 circuit combiner
mountable down to a 3/12 pitch for AC micros at 240VAC. They have a
fingered buss bar that has offsets to catch every other pole on the dual
pole breaker sets.....in addition it has their external lockable, visible
disconnect on the exterior of the box.......
So am discovering that there are options......I will probably use the
midnite solar option as the breakers are a small fraction of the cost of
the breakers used int he Soladeck...
Thanks for all the help...
Cheers,
Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-299-0402 o
On Wed, Apr 23, 2014 at 1:23 PM, Jason Szumlanski <jason at fafcosolar.com>wrote:
> While the interior of a raceway in a wet location is considered a wet
> location, the interior of a NEMA 3R enclosure is not. The breakers need not
> be listed for use in wet locations. That's the interpretation of all area
> AHJs here, and there is tons of evidence to support this logical conclusion
> (NM cable into exterior mounted NEMA 3R disconnects, switch enclosures;
> NEMA 1 enclosures inside larger NEMA 3R enclosures, etc.)
>
> I hope I didn't just open a can or worms... :)
>
> Jason Szumlanski
>
> Fafco Solar
>
>
>
> On Wed, Apr 23, 2014 at 3:12 PM, Glenn Burt <glenn.burt at glbcc.com<glenn..burt at glbcc.com>
> > wrote:
>
>> Are these breakers listed for use in wet locations?
>>
>>
>>
>> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
>> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jason
>> Szumlanski
>> *Sent:* Wednesday, April 23, 2014 1:51 PM
>> *To:* chris at solarandwindfx.com; RE-wrenches
>> *Subject:* Re: [RE-wrenches] Stainless NEMA4x load center, SolarDeck w/
>> breakers
>>
>>
>>
>> Here is exactly what I ordered:
>>
>>
>>
>> (1) RST0760-41AD Soladeck AC/DC Combiner Box
>>
>> (1) RST0784AC-3K Soladeck AC 3 Circuit Busbar Kit
>>
>> (2) RST1455.20 ABB Mini Circuit Breaker 120/240VAC 20A
>>
>> (1) RST1455.15 ABB Mini Circuit Breaker 120/240VAC 15A
>>
>> (1) RST1440..080 Soladeck Power Block 600V 80A
>>
>>
>>
>> This model has a cover that is bumped out to fit breakers. Here is a
>> pic of the closed up box.
>>
>>
>>
>> [image: Inline image 1]
>>
>>
>>
>> Again, I'm not really happy with the way I brought the Enphase cables
>> into this Soladeck. The knockout center-points provided by the
>> manufacturer are too close together to accommodate five water-tight
>> glands, so I used some offsets to make more space. If it wasn't my own
>> house, I would have wanted it to look much prettier for a customer.
>>
>>
>>
>> One thing I highly recommend is along the top and sides to use sealant as
>> indicated in the manual, then sprinkle a generous amount of granules in the
>> sealant. Otherwise the cover and your fingers get gummed up when taking the
>> cover off.
>>
>>
>>
>> The manufacturer's website and documentation is woefully inadequate for
>> this product. They need to clarify it, obviously, based on this discussion
>> if they want to sell more. It's a great solution IMO.
>>
>>
>>
>> Jason Szumlanski
>>
>> Fafco Solar
>>
>>
>>
>>
>>
>> On Wed, Apr 23, 2014 at 12:01 PM, Chris Schaefer <
>> chris at solarandwindfx.com> wrote:
>>
>> Jason,
>>
>> I love the picture. Just ran into this a few days ago on an
>> install. Had two older SolarDeck Model 0780 in stock. I had the same two
>> pole breakers and attempted to install them here in the shop before I went
>> out to the project as I was afraid their height would not allow the cover
>> to seal. And it did not. It appears you have ABB breakers and I just tried
>> them and they don’t fit either. Now if you look at your link it shows and
>> states fuse holders, which do fit. I’m wondering if the newer models in
>> your link are just a little bit taller than the older models I had in
>> stock. I don’t see size specs on their web site. Can you please provide the
>> model# you show in your photo?
>>
>>
>>
>> Christopher Schaefer
>>
>> Chris Schaefer’s
>>
>> [image: SolarWindFX]
>>
>> * Tel/Fax 585-229-2083 <585-229-2083> or Cell
>> 585-748-1870 <585-748-1870> *
>>
>> * 5115 South Hill Road ~ Canandaigua New York 14424*
>>
>> *www.solarandwindfx.com <http://www.solarandwindfx.com> ~ E-mail:
>> chris at solarandwindfx.com <chris at solarandwindfx.com>*
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to
>> exist
>> when you take away from those who are willing to work
>> and give to those who would not."
>>
>>
>>
>> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
>> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Jason
>> Szumlanski
>> *Sent:* Wednesday, April 23, 2014 11:36
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] Stainless NEMA4x load center
>>
>>
>>
>> See my other response, but you should definitely consider SolaDeck in
>> this case.. You want SolaDeck Model 0786-41. Make sure you order the
>> correct breakers, bus bars, and Neutral terminal block.
>>
>>
>>
>>
>> http://www.rstcenterprises.com/soladeck/products/1741_combiner_enclosure.phtml
>>
>>
>>
>> The attached picture is the Soladeck on my 3-string Enphase system at
>> home (note: neutral block was not on DIN rail yet). There are four neutrals
>> on the bottom of the N block because I center-fed one inverter string, so I
>> had four sets of Enphase cable coming into the box, which is admittedly a
>> little tight. If you need to do this, I recommend transitioning to THWN in
>> a separate combiner and just bringing in three strings through one or two
>> conduits.
>>
>>
>>
>>
>>
>> [image: Inline image 1]
>>
>>
>>
>> Jason Szumlanski
>>
>> Fafco Sola
>>
>> r
>>
>>
>>
>> On Wed, Apr 23, 2014 at 11:17 AM, Kirpal Khalsa <solarworks at gmail.com>
>> wrote:
>>
>> Drake.....we want it to mount flush to the slope of a sloped roof....The
>> NEMA 3R are supposed to be mounted vertically....This is for a large
>> residential Enphase system and we wanted to combine the circuits on the
>> roof and bring one set of conductors down.....
>>
>> I did find one custom made by Eaton(Cutler Hammer), but....$952 my cost
>> is too much..I have had them make me one out of fiberglass in the past but
>> it is about 3 years into its roof mount life and showing signs of UV
>> degradation...looking for other options....I think i will dig a little
>> deeper at Midnite Solar.....They may have something....Theirs and Outback's
>> PV combiners are rated to be mounted at a slope....i think it is down to 14
>> degrees pitch (3/12)
>>
>> Thanks.
>>
>>
>> Sunny Regards,
>> Kirpal Khalsa
>> NABCEP Certified PV Installation Professional
>> Renewable Energy Systems
>> www.oregonsolarworks.com
>>
>> 541-218-0201 m
>> 541-299-0402 o
>>
>>
>>
>> On Wed, Apr 23, 2014 at 8:11 AM, Drake <
>> drake.chamberlin at redwoodalliance.org> wrote:
>>
>> That would be a nice piece of hardware. Is there any reason you can't use
>> a NEMA 3R panel? They are used on roofs quite a bit, and are readily
>> available. The Square D, 8 space, outdoor box should work in most rooftop
>> environments for the purpose you describe.
>>
>>
>> At 06:18 PM 4/21/2014, you wrote:
>>
>> Hello Friends!
>> Anyone have a lead for* NEMA 4x* stainless load centers (electrical
>> panel)? Â Looking for 4 circuit version rated at about 60-100A @ 240VAC.
>>
>>
>> Would like to use it for rooftop combiner for 3 Enphase inverter output
>> circuits.
>> Thank you!!
>>
>> Sunny Regards,
>> Kirpal Khalsa
>> NABCEP Certified PV Installation Professional
>> Renewable Energy Systems
>> www.oregonsolarworks.com
>> 541-218-0201
>>
>> ______________
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 130249 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 24285 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 2415 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 251224 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 2593 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 2759 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140423/40ac7a8d/attachment-0002.jpg>
More information about the RE-Wrenches
mailing list