[RE-wrenches] Three Inverters, One Disconnect?
Garrison Riegel
garrison at solarserviceinc.com
Wed Apr 2 18:20:36 EDT 2014
Hello Wrenches,
On an upcoming project we are interconnecting (3) Power-One, ahem, ABB PVI
3.6 inverters to a 3Ph 277/480V service. Each inverter output is 16A at
277V, 1Ph. Is it code compliant to run the single phase output of each
inverter to a single pole of a 3-pole [utility required] AC disconnect
before landing at each 1-pole 20A breaker in the main panel? It would be
great to avoid an inverter subpanel and 3-pole breaker in the MDP if
possible.
Thanks for your thoughts.
Garrison
Garrison Riegel
Project Manager | <http://www.solarserviceinc.com/> Solar Service Inc
[p] 847-677-0950 | <mailto:garrison at solarserviceinc.com>
garrison at solarserviceinc.com
NABCEP Certified PV Installation ProfessionalT
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140402/e4116598/attachment.htm>
More information about the RE-Wrenches
mailing list