[RE-wrenches] Unusual problem with SMA TL inverter on metal roof
boB at midnitesolar.com
boB at midnitesolar.com
Fri Mar 14 02:19:56 EDT 2014
Interesting app note. Interesting problem.
How far from this metal roof (grounded I presume) is the bottom of the
modules ?
This app note is mainly talking about the area of the module from the
mounting bracket which should
be quite a bit less than the modules area from a distance above a
grounded metal plate like this roof.
How far above the metal roof are the modules ? If they are real close,
raising them slightly might
be enough to lower that capacitance enough to stop the TL from tripping.
Another thing you could do, but would of course cost money would be to
split the array up for
more inverters.
This app says that 1400 nano-Farads is an approximate point for
problems. That's for 50 Hz.
It will be around 6/5 worse at 60 Hz.
If you have a capacitance meter (impedance bridge or meter), you could
measure the capacitance
of the array. Disconnect the + and - from the inverter first of
course. Then, tie the plus and
minus of the combined array together and connect that to one terminal of
the capacitance meter.
Connect the other lead of the capacitance meter to the roof and/or
ground and it ~should~ show
the capacitance you are interested in.
This is one of those newer compromises associated with the higher
efficiency TL inverters (anybody's,
not just SMA's of course), and also the newer code requiring TL
(non-isolated) inverters above 300 volts
and everything else new we have to all learn about.
Welcome to the future ! ( from Firesign Theater's "I think
we're all [solar] bozos on this bus" )
boB
On 3/13/2014 7:31 PM, Marco Mangelsdorf wrote:
>
> Friends,
>
> We have run across an odd technical problem at our commercial install
> at a laundromat on our island. Attached is the description of the
> issue from SMA. We don't know much except that we are switch out the
> TL inverters to the old style US inverters because SMA has no fix for
> the phantom ground tripping. The issue is beyond our feeble
> understanding.
>
> Any observations to share?
>
> Thanks,
>
> marco
>
>
-------------- next part --------------