[RE-wrenches] 690.13(A) Mistake?
Nathan Charles
ncharles at paradiseenergysolutions.com
Tue Mar 11 15:54:17 EDT 2014
Hi Wrenches,
So I was reading through the handbook today and got confused on the
exception to 690.13 which reads:
690.13(A) Exception: Installations that comply with 690.31(F) shall be
permitted to have the disconnecting means located remote from the point of
entry of the system conductors.
That should actually be 690.31(G) correct?
Best regards,
--
Nathan Charles
Engineer
NABCEP Certified PV Installation Professional #042013-20
Paradise Energy Solutions
(717) 283-2021 direct
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140311/b77295f8/attachment.htm>