[RE-wrenches] conductors and the 120% rule
Kirk Herander
kirk at vtsolar.com
Tue Mar 4 12:05:23 EST 2014
Hello,
I have a 225 amp 3-phase main lug sub-panel protected by a 200 amp breaker.
My inverter breaker feeding the sub panel is 60 amps. So 225 a bus x 1.2 =
270 amps. That's less than the sum of the two breakers of 260 amps, so no
issue there. The conductors between sub and main panel have to be rated for
at least 260/1.2 = 217 amps, correct? Is this 217 amps before or after
derating the conductor?
Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified Inaugural Certificant
NYSERDA-eligible Installer
VT RE Incentive Program Partner
802.863.1202
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20140304/b9e26732/attachment.htm>
More information about the RE-Wrenches
mailing list